    Good job, baffin. So now you finally understand that MOVs don't WEAR. Or do you?
    Your tires wear. Your brakes wear. That's a normal in-service condition the designer fully expects and accounts for. The device still meets spec and performs as intended after significant wear. Your window glass doesn't wear. If it takes a hit, it's either OK or broken. Same with MOVs. That's why they put LEDs on the better ones, so you can tell if they're OK or broken.

  2. #28
    Join Date
    Aug 2004
    Posts
    29
    Post Likes
    http://www.surgex.com/library/92001.html

    Dx, Your still wrong. Do a search on "MOV DEGRADATION".
    MOV's are DEGRADED, or should I say WORN, by surges over the designed max. Temporary over voltages from the utility, say 140 volts instead of 120, for 10 seconds or more will cause significant WEAR on the MOV's in most of the surge strips found in stores today (MCOV of 130V). It won't toast them, but it will reduce the voltage at which it passes current. Since it begins clamping at a lower voltage than initially designed, it's peak current handling rating for it is also lower. In other words it's not as good as it was when it was new because it's WORN.

  3. #29
    Join Date
    Jul 2005
    Posts
    171
    Post Likes
    Originally posted by baffin789
    [url]
    MOV's are DEGRADED, or should I say WORN, by surges over the designed max.
    No you should NOT say WORN. You should say degraded, failed, broken, replaceitnow, goodbye, sayonara, adios.

    This is common sense. If you exceed the design max of your double-pane window and break only one pane, it still kinda keeps the rain out. But it's not WORN, it's BROKEN.

Page 3 of 3 FirstFirst 123

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech 365