    I have a customer that claims there is a a low wear belt recommended for Data Centers. He get his Data Center Cleaned once a year and is telling me that the belts I have been using on the maintenance are releasing to much belt dust causing his Data Center to get dirty. What is a good brand of belt to use in a Data Center that will release less belt dust/residue. I have been using the Gates brand and have everthing at the correct belt tension and alignment. My sheaves and pulleys are in good shape no deep groove or signs of slippage. Any advice would be appreciated.

  2. #2
    Join Date
    Apr 2007
    Location
    USA
    Posts
    781
    Post Likes
    thats a first for me. The only time I have seen belts give off enough junk to cause complaints was caused by the pulley.
    We use BX belts from Browning. Are you sure it is the belt? Do you have belt residue around the fan? Does the indoor blower run all the time? Is belt/pulley system properly sized?

  3. #3
    Join Date
    Sep 2002
    Location
    Hampton Roads, Virginia
    Posts
    2,062
    Post Likes
    Why not offer to upgrade them to synchronous belts? Always look at every job as an opportunity to upsell.

    Kevin

    Controls is a lifestyle not a job

  4. #4
    Join Date
    Jun 2005
    Location
    Portland Oregon
    Posts
    85
    Post Likes

    Cool

    I use the Liebert VT belts on everything I can, they are a low stretch, low dust belt and are matched sets. They are made by browning for Liebert units. I can't say enough about these things. Also I recommend (if you have not already) get rid of any variable pitch pulleys and any that have grooves starting, they're just a belt grinder. Put in fixed pitch and put the time in to align the pulleys right. That also means that you may have to shim the backside of the motor to compensate for the pull of the belts. You know you did it right when you come back on the next maintenance and the paint has not worn off the pulleys yet.

    If you have any questions you can e mail me and I can send you some VP to fixed pitch conversion paperwork.
    do things right the first time is cheaper.

  5. #5
    Join Date
    Apr 2011
    Location
    Austin, TX
    Posts
    2
    Post Likes
    I have run into this exact problem before. 12 CRAC's running and somebody decided to save 5$ a pair a buy cheap belts. 2 months later we have black dust build up on the inlets of our servers. We moved to coggless belts, laser pulley/sheave alignment, and I think Goodyear belts. Also replaced all pulley's sheaves that appeared to have any "grooving" whatsoever. Worked for us, but I don't have a specific belt recommendation that is purely "dust free"

  6. #6
    Join Date
    Jul 2011
    Posts
    3
    Post Likes
    We are on i data center facility but i am not sure of what belt they are using..

  7. #7
    Join Date
    Jan 2008
    Location
    melbourne aus
    Posts
    80
    Post Likes

    liebert belts?

    g' day fridgies
    As all the other guys have said, dont go cheap on the belts, make sure all pulleys are in good nick, and are alighned properley.

    What are the liebert vt belts I have never heard of them and UI have only seen emerson put on normal gates belts.did you get the belts from emerson? I used to look after a site that had 50 cracker units and the dust was starting to become an issue. some one before me had up sized the belts from A section to B section belts to stop the dust, this had a secondry effect of making the motors pull more amps and up goes power consumption.

  8. #8
    Join Date
    Jul 2011
    Posts
    3
    Post Likes
    Quote Originally Posted by klrogers View Post
    Why not offer to upgrade them to synchronous belts? Always look at every job as an opportunity to upsell.

    Kevin

    yes he's right! Data Center will get more efficient if the components are periodically changed and upgraded.. the newer the better.

  9. #9
    Join Date
    Feb 2011
    Location
    Georgia
    Posts
    872
    Post Likes
    any belt should be fine. get a tab company to check your shivs and alignment. the wear could be due to misalignment

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •