Folks, we are trying to develop standards in developing professional control design submittals....can you give me some ideas on how you do the following
1) symbols ...Temp -pressure or humidity sensors..how do you define these in the symbols page....besides the physical shape do you assign code numbers?
2) system drawing device callouts...assuming you show a device to represent say a temp sensor...do you assign a code to this IE T1-T2..and then a point name ?..do you number these sequentially.....what if you have thermisters and rtd's.....do you use the same code or callout numbers for the same type of sensor from job to job ?....
3) how do you link the sensor device on drawings to the control panel termination locations....so it would be easy for an electrician to install by ?
thank you in advance for any suggestions.....really appreciated
05-19-2011, 07:20 PM #2
Are you/do you work for a controls contractor? If so you might check the product line you rep. Many product lines have a lot of this in place in which it makes your life easier.
"How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue
BIG Government = More Dependents
http://threedevilskennel.com/ - not my website.
Versatile Hunting Dog Federation - www.vhdf.org/
05-19-2011, 07:38 PM #3
One of the best specification building websites is www.ctrlspecbuilder.com
Generates specs, sequences and drawings. In editable Word, autoCAD, Vision and pdf.
kontrol out"Can't we all just get a Lon?" - Garry Jack
"BACnet: integration or interrogation?" - The Janitor
"Open protocols? You can't handle open protocols!" - Nathan R. Jessup
“What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE
05-19-2011, 11:18 PM #4
- Nov 2006
- Desert Southwest
- 369
05-20-2011, 09:36 PM #5
- Jan 2008
- Near Philly
- 382
This is A typical of what I submit, I usually have little trouble with the project engineers.
05-21-2011, 02:48 PM #6
- Feb 2009
- Whitby, Ontario
- 15
Controls submission standards
Hi. I am the senior engineer for the largest owner operated controls contractor in a major Canadian market.
My expectations for a set of shop drawings would include
- symbols are ASHRAE symbols - no need to reinvent the wheel
- a legend of symbols
- a controls schematic for each system
- a sequence of operations for each system
- a bill of materials for each system, and the overall project
- a DDC points list for each controller, sorted by function
- a valve schedule
- a motorized damper schedule
- an index
- a collection of standard wiring diagrams for various point types.
We (and everyone else I know) use Microsoft Visio software and tabloid sized paper.
However much effort you put into shop drawings, you will always run into a consultant that has some additional request , so your style will evolve.
BTW good shop drawings are conducive to predictable installation costs and smooth startups.
http://hvac-talk.com/vbb/images/smil...eers:eers2.gif
05-22-2011, 12:43 PM #7
- Oct 2003
- Minnesota
- 1,125
Pretty close to what we do.
For the original poster ...
Take a look at this just for some ideas:
http://cid-0554c074ec47c396.office.l...t%20100000.pdf
We use Visio, Excel, and Word but I converted everything to a PDF format so you can see a sampling of how we do things.
Of course, it's not the complete submittal, and deatils about what project, what customer, etc have been removed.
But it shows a cover sheet and table of contents, some of the points sheets for each controller, some of the schedules, and some of the drawings.A site where I stash some stuff that might be interesting to some folks.
http://cid-0554c074ec47c396.office.l...e.aspx/.Public
] .....what if you have thermisters and rtd's.....do you use the same code or callout numbers for the same type of sensor from job to job ?.... SURE BUT WE NEVER MIX THE TWO ON THE SAME JOB, WELL ALMOST.