Results 1 to 13 of 18
    Dec 2010
    N 37° 10.573 W 093° 15.649
    Honeywell T-Stat Spec Software
    I have a large project at Fort Leonard Wood involving Honeywell T7350A’s and T7350H’s. I have configured these with the T-Stat Spec software I downloaded off Honeywell’s website. My question is, when you are configuring the schedules, say if you have a building occupied Mon-Fri 0600-1730 with Sat and Sun un-occupied, do I leave Sat and Sun “un-configured”? Does the un-configured setting on those days make the space run off the un-occupied setpoints or is there a way to make those two days un-occupied all day without making them occupied for one minute a day then returning to un-occupied. I just don’t want the stat to go through optimal start/stop for 3 hours previous to a one minute occupied period during weekend days.
    This is a very large project involving hundreds of buildings, sold to the Gov't to conserve energy, so as much as I can conserve the better for them and me!
    When it is said that BacNet is a better protocol than LonWorks, I die a little more inside.
    ~knottyjabe
    Western Oregon
    I believe un-configured time slots will follow the mode of the last configured time slot.
    RealEyes
    Realize
    RealLies!
    Feb 2007
    Helena, Montana
    They don't have a base-wide EMCS?
    Don't worry zombies are looking for brains, you're safe...
    Mar 2006
    Loytec can do it.
    Western Oregon
    Third!
    RealEyes
    Realize
    RealLies!
    Dec 2010
    I just got an anwser back from Honeywell and they said it will follow the current state until the next change of state, so weekends set for un-configured preceded by an un-occupied will remain un-occupied for the whole weekend. Thanx RAD1
    ~knottyjabe
    Dec 2010
    Quote Originally Posted by ControlsInMT View Post
    That is what this project is...
    ~knottyjabe
    Feb 2007
    Helena, Montana
    Quote Originally Posted by knottyjabe View Post
    Wow. There are a lot less expensive and flexible ways than using those, but if that's what's spec'd....
    Dec 2010
    Yea, agreed, but you can't talk those people into anything different, like you said spec's spec!
    ~knottyjabe
    Dec 2010
    Thanks to all for your help, my last issue with this is; if it is saturday(schedule is set as un-configured but in un-occupied, looking for a change of state on monday at 0600), and someone comes in to do some weekend work, and presses the "temporary occupied" button, the stat will go temp occupied for a set amount of time, when this override time expires does the stat go back to un-occupied or does it stop all control and wait for monday at 0600 when it will return to occupied mode?
    ~knottyjabe
    Feb 2007
    Helena, Montana
    I can't find anything that actually answers that. Logic would think it would go back to last known state, which would have been unocc, but I couldn't verify it.
    Western Oregon
    Covering ALL the bases aren't you knottyjabe? I don't blame you! I agree with ControlsInMt, don't know for sure in this instance but logic says...
    RealEyes
    Realize
    RealLies!
    Dec 2010
    These questions are just paranoia, I have configured and installed these about 3 mos ago, and started thinking-hey, what if- I have had no complaints or issues but I also want them to be right, ya know. This project involves so many buildings, I just don't want to have to go back and alter configs on every building!
    ~knottyjabe
Tags for this Thread