    I need some help. This is my first wshp ive worked on. the problem is the unit cuts on for about 30 seconds then shuts off like its tripping pressure switch. i checked the normal things high pressure switch, low pressure switch. i call tech support for help and according to them the board is indacating low temp switch which i bypassed. same problem still. installers did not leave manual for unit so i cant determine what the diagnostic code is on the board. yellow led flashing rapidly non stop. if anyone could help me i appreicate it. i need to have unit running in morning.model# is fcu060blfr

  2. #2
    Join Date
    Oct 2003
    Location
    South Carolina
    Posts
    1,242
    Post Likes
    How's the water flow through the heat exchanger?
    “Two things are infinite: the universe and human stupidity; and I’m not sure about the universe.” —Albert Einstein

  3. #3
    Join Date
    Jan 2010
    Posts
    8,193
    Post Likes
    I see one post has been deleted for DIY. Are you in the trade ?

  4. #4
    Join Date
    Jul 2008
    Location
    Southern California
    Posts
    142
    Post Likes
    Yellow flashing light on Mcquay WSHP is low temp. Is it tripping in heating or cooling ?

  5. #5
    Join Date
    May 2011
    Location
    charlotte nc
    Posts
    93
    Post Likes
    its in cooling mode and yes ive been a tech for 3 years this is just my first wshp

  6. #6
    Join Date
    Sep 2009
    Location
    Boyertown, Pa
    Posts
    50
    Post Likes
    Check the sensor in the drain pan for high water/ clogged drain line. I had a similar problem and there isn't a fault code for it.

  7. #7
    Join Date
    Jul 2011
    Location
    indiana
    Posts
    60
    Post Likes
    Check your loop temperature. If your supply water is to cold, system will trip on cold water safety. Also check tempersture sensor; but i doubt it is a sensor. There should be sticker on the side of control panel indicating all faulty codes. Also check on line. Dont give up easy. Good luck.