Results 1 to 3 of 3
  1. #1
    Join Date
    Oct 2007
    Location
    Huntsville, AL
    Posts
    395

    Trane VariTrac 2 CCP

    I am trying to connect to a CCP using HyperTerminal. If I look inside the CCP I see the dip switch for the baudrate is set to on which makes the baudrate 1200 so I connect to it at baud rate 1200 and I get the VariTrac screen that tells me to hit h for help and L for list but no matter what I hit I get nothing! Has anyone else seen this problem before?


    Im like a mushroom, they keep me in the dark and feed me crap.

  2. #2
    Join Date
    Jun 2004
    Posts
    727
    Try capslock or no capslock.

  3. #3
    Join Date
    Oct 2007
    Location
    Huntsville, AL
    Posts
    395
    I finally figured it out, I had my flow control set to hardware opposed to none...


    Im like a mushroom, they keep me in the dark and feed me crap.