Results 1 to 6 of 6

Thread: AX Lon Links

  1. #1
    Join Date
    Oct 2007
    Location
    England
    Posts
    144

    AX Lon Links

    I need a bit of clarification for my ever thickening brain.

    If I make lon links in the link manager from a device back onto itself (nvo to nvi) which is connected to a Lon network with a Jace as the Lon network manager.

    So long as I have performed a 'Bind' on the links; and possibly commission the device, I could then technically switch off the Jace and the links would still work. Yes?

    I.e. the device would then work stand alone sending data back onto itself.

    This is how I would expect it to work but I cannot find any information about this in Doc Lonworks.

    Thanks
    Keith

  2. #2
    Join Date
    May 2002
    Posts
    9,564
    LON is a peer to peer network.

    Are you familiar with LNS LON? (NL220, lonmaker, Circon NI, Lonwatcher, etc..)
    Do you walk away from the site with your software after you are done?

  3. #3
    Join Date
    Oct 2007
    Location
    England
    Posts
    144
    I thought as much.

    But someone posed me the question today and I said that I was pretty sure that if the Jace failed then the system should operate as pretty much as normal.

    I then said I would double check though just to make sure. And sure enough I couldnt find a definitive answer.

    Keith

  4. #4
    Join Date
    May 2002
    Posts
    9,564
    Well, the protocol is ISO 14908. If they are using it they need to make reasonable attempts to use it correctly.

  5. #5
    Join Date
    Dec 2007
    Posts
    90
    Any proxy linked points would be gone. for example let's say you link OSA from one controller to another but do it from proxy points under the point folder to proxy points under another devices point folder, those are in the Jace and go where the Jace goes. But if you link device with OSA direct to other device, that will stay. Like sysint said hinted to, links need to be done with thought and correctly for the desired outcome.

  6. #6
    Join Date
    Nov 2007
    Location
    Phoenix, AZ
    Posts
    256

    Links

    Quote Originally Posted by Keith D View Post
    I need a bit of clarification for my ever thickening brain.

    If I make lon links in the link manager from a device back onto itself (nvo to nvi) which is connected to a Lon network with a Jace as the Lon network manager.

    So long as I have performed a 'Bind' on the links; and possibly commission the device, I could then technically switch off the Jace and the links would still work. Yes?

    I.e. the device would then work stand alone sending data back onto itself.

    This is how I would expect it to work but I cannot find any information about this in Doc Lonworks.

    Thanks
    Keith

    Yes, the link is in the network. Just like a link in Lonwatcher or Lonmaker. After you link the device to its self or device to device, bind turn off the jace and take it away if you want, it will still keep working.

    GregF

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •