    Mar 2010
    Kelowna, BC
    Possible Upgrade to Delta Controls Stat RTS-406?
    I am servicing a hotel that has an old Delta Controls system in it. It has about 90 rooms in it all with the Delta RTS-406 themostat. Many of the thermostats are failing, plus they are ulgly old things.
    Does Delta make another thermostat that will directly replace this antique? Will the DNS-24 line work?
    What communication protocol do the RTS-406 thermostats work on?
    Thanks for any help
    Rick
    Dec 2006
    What? Who? Where?
    It appears that the RTS-406 is an obsolete zone sensor for Delta V2 system. It uses a different protocol than the DNS-24. There is a replacement RTS-242 (which uses the DNS-24 hardware) that uses the correct protocol for replacement. Also note that the RTS-406 uses 8VDC to power it where as the RTS-242 uses 24VAC. You might have to revise the programming in the controller as well.
    kontrol out
    "Open is as open does." - Forrest Gump
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE
    Oct 2009
    Nova Scotia, Canada
    Just to add to Kontrol's post. The replacement is actually the RTS-424. As was already stated you will need a seperate power source.
    Dec 2006
    What? Who? Where?
    CE-TECH is correct, interwebby dyslexia on my part.
    kontrol out