Results 1 to 10 of 10
    Jan 2011
    Ohio Valley - St Clairsville
    Replacing filter drier?
    I'm working on a Carrier 50TFQ006 heat pump package unit. Found unit out of r-22. Found major leak on the suction line. Repaired and pressurized with nitrogen till monday. This unit has two factory installed filter driers (the small copper cylinder type) in their respective liquid line each with a check valve brazed in next to it. These lines run vertically and are all compact with the condenser and evaporator headers. I may be able to replace one with a c-163s with some repiping but there isn't even room to replace the other with a c-083s. Does anyone have any recommendations?
    Jul 2009
    In a mechanical room....
    So your having trouble installing a dryer.....
    This site is no DIY
    “It takes courage to grow up and turn out to be who you really are.”
    - E.E. Cummings
    Aug 2005
    iowa
    maybe it could be installed in a differant location? up or downstream from the current location?
    it really needs to be replaced (im sure you know that since you asked) think outside of the box...... maybe literally
    jeep
    Oct 2007
    Richmond, VA
    Both can be fit in there, but not in their existing location. You'll have to pipe them away from where their at. Also, replace the check valves while you're at it.
    Also, fill in you profile information and get your post count up and apply for pro status. Oh yeah, welcome to the forum.
    Jan 2011
    No ho diy. Professionally paid diy. Just newer to this site and have been doing commercial hvac service for two years now. I'll have to get a better look at it monday. A 163 does up to a 5 ton so in replacing both do I replace both with a 163? or 083? with this being a heat pump. Thanks for the replies.
    Jul 2009
    Can't ya just stager the two dryers pipe them a little different?
    - E.E. Cummings
    Jan 2011
    Quote Originally Posted by chrishvacman View Post
    It's definately gonna have to be piped differently, the two lines aren't side by side. More like liquid line, condenser header, liquid line (backed into a corner), evaperator header, accumalator. LL's running vertically. All this is compact, definately some heat exchange going on in there. LOL. Like I said get a better look Monday.
    Amazing Grace, it is amazing!
    Oct 2007
    Richmond, VA
    Quote Originally Posted by ewwilt View Post
    You'll want to go with the 163 driers. You need 5 ton capacity in either direction.
    Jul 2010
    napping on the couch
    Lennox has filter driers with built in check valves. They take up less space.
    Here is the 083 model. I'm pretty sure there is a 163 model
    http://www.plccenter.com/Buy/LENNOX/78A8801
    Call Lennox and see if they can help you out.
    Lennox does say this can handle up to a 5 ton unit, but I'd be concerned putting the 083 in a 5 ton unit though.
    “Free men do not ask permission to bear arms.”
    -Possibly said by Thomas Jefferson(but true even if he didn't)
    “What one generation tolerates, the next generation will embrace.”
    ― Definitely said by John Wesley
    "One out of 3 Democrat voters is just as stupid as the other two"
    -Said by me
    Jan 2011
    I got the filter driers changed out the other day. 163 on the cooling circuit and 053 (163 was not even fitting in there) on the heating circuit. Yeah 053 not quite ideal but better than what was there. Thought reasoning was this is going to be running in cooling mode for quite a while and will help get the system cleaned - dehydrated as needed before it runs heating. Evac to 365 microns. Cooling and heating good now.
    Thank you guys for all the input. (root beer)