Results 1 to 5 of 5
  1. #1
    Join Date
    Aug 2005
    Posts
    1
    Post Likes
    I have an Evcon fossil fuel kit (3024-7481-E) with a coleman/evcon two bulb mercury stat. There's a york heat pump, paired with a coleman furnace. I'd like to put on a honeywall stat, but can't figure out exactly what is what.
    I know what the r,y,g,and o are. I'm just not sure what w2, B, X, and L are on the old stat. I would assume one is for the heat pump heat, and one is for the gas/emergency heat, but can't figure it out for sure. please help.

  2. #2
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    3,022
    Post Likes
    R = Power
    Y = Compressor Contactor
    G = Furnace/airhandler fan
    W2 = Second Stage Heat, most likely used to run the furnace instead of heatpump in your case
    W = Normally regular heat

    For the heat from the pump, the circuit between Y and R is closed. O is the reversing valve - it is energized along with Y when cooling only.

    I suggest that you call a technician. Wait for someone else to verify the info posted here.

  3. #3
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    38,999
    Post Likes
    Heat pump stats are confusing. We make good money cleaning up after HO's try to wire their own!

    From what I see in my HP stat cross reference book, B is used for defrost on some old units. I'd skip it. X is common, sometimes B and sometimes C. L is a fault light, rarely used.

    Follow at your own risk. If you fry something, you're on your own!

    Personally I'd try to find a Honeywell Vision (home stores) or Vision Pro (sold through dealers).

  4. #4
    Join Date
    Sep 2001
    Location
    Vancouver Canada
    Posts
    996
    Post Likes
    Go with a vision pro tstat, have to be a contractor model as you will need one with 2 stages of heat to run both the furnace and heatpump. If you go with a vision pro you can ditch the fossil fuel kit and use a outdoor temp sensor wired to the thermostat to cut out the heatpump and changeover to furnace when temps are below the temp you program. They work very well and are extremly easy to program.
    "Go big or Go Home"

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,863
    Post Likes
    Call a contractor, you don't want to pay for the more expensive repair if you short out the boards in the furnace or heat pump.

    In order to use a vision pro properly with its duel fuel set up, the fossil fuel kit would need to be btpassed.

    This is NOT a diy project.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.