Results 1 to 4 of 4

Thread: Trane Tracker

  1. #1
    Join Date
    Aug 2005
    Posts
    11
    Post Likes
    Having problem with ZN517 controller communicating with Tracker panel. System has three controllers for three units. Tried to rebind this control but did not work. ZN517 is controlling the unit but cannot be viewed on Tracker panel. I also checked the communication wiring between controllers and tested outputs of ZN517. All checked OK. Job was installed two years ago and has not had any problems until this one. Thanks for any replies.

  2. #2
    Join Date
    Jul 2005
    Location
    Orange County, NY
    Posts
    936
    Post Likes
    Have you tried the "Wink" command?

    Core

  3. #3
    Join Date
    Aug 2005
    Posts
    11
    Post Likes
    Thread Starter
    Not sure what that is! Please explain! THANKS

  4. #4
    Join Date
    Jul 2005
    Location
    Orange County, NY
    Posts
    936
    Post Likes
    Hello bgcas

    If you take the cover off of the ZN517 you will see a small "Push Botton" you need to locate that button.

    First go to the Tracker main panel and get to the screen that allows you to search for new controls.

    Activate that command.

    Go to the ZN517 and push in that service button.

    Go back to the Tracker panel and the system should update.


    Core