Thread: Trane Tracker
    Aug 2005
    Having problem with ZN517 controller communicating with Tracker panel. System has three controllers for three units. Tried to rebind this control but did not work. ZN517 is controlling the unit but cannot be viewed on Tracker panel. I also checked the communication wiring between controllers and tested outputs of ZN517. All checked OK. Job was installed two years ago and has not had any problems until this one. Thanks for any replies.
    Jul 2005
    Orange County, NY
    Have you tried the "Wink" command?
    Core
    Aug 2005
    Not sure what that is! Please explain! THANKS
    Jul 2005
    Orange County, NY
    Hello bgcas
    If you take the cover off of the ZN517 you will see a small "Push Botton" you need to locate that button.
    First go to the Tracker main panel and get to the screen that allows you to search for new controls.
    Activate that command.
    Go to the ZN517 and push in that service button.
    Go back to the Tracker panel and the system should update.
    Core