    Jul 2005
    ahu trane m#twe060c15fdo s#44355y52v 75' ahu 20'higher then cond. pipes 1/2'liquid 11/8 suction unit down smoke detector started unit 62/320psi found ahu is heatpump/but condensor not,unit is cooling.liquid line cool to touch.going back monday any suggestions
    yeah, call a pro.
    I`m not real sure what you are asking????????
    Jul 2005
    billva gess your not a pro/i've been doing this 15 year,can always learn something.thinking i have to look for restriction
    Is it a new install.
    If not, have you cleaned the condenser coil.
    What type of metering device.
    Whats the indoor wb
    The outdoor db.
    What was the superheat.
    What was the subcooling.
    Need alot more info then you posted.
    Are you new to the trade.
    sorry for the comment.
    high head w/ low suction, first, clean the condenser coil even if it "looks" clean.
    second, do that and then give new pressures and temps.
    third, all temps.
    Jul 2005
    txv,5 month old system,os temp 95 comp.amps 27 cond. fan ok evap.ok
    Jul 2005
    didn't take superheat had to go to another job ,know i be back this monday
    Pull the sensing bulb of the txv, and warm it up and see if the suction pressure changes.
    Are these the readings you found when you got there, or did you add gas.
    you had time to put your gauges on but no time to put a thermometer on the suction line?
    Jul 2005
    if you read my first message the unit was off smoke detector.unit been running this way,most likely from start up and person walk away.
    Your OP, kinda runs together.
    I got 75' lineset, a/h 20' above condenser.
    And the pressures.
    And off by smoke detector.
    But you didn't include anything else you did.
    Knowing the pressures alone is meaningless without knowing the superheat, subcooling, outdoor ambient temperature, and return air dry bulb and wet bulb temperatures.