    Dear all,
    For commercial buidling, what is ventilation rate for washroom? (Ashrae requirement)
    250 sqft, assume 2 persons there
    Thanks!
    [Edited by wyblueheart on 08-11-2005 at 11:51 AM]
    Apr 2002
    For a washroom used by the public, ASHRAE would typically require 50 cfm per water closet and urinal.
    The Standard Mechanical Code dictates 2 CFM per square foot of floor space.
    http://www.ductstrap.com/
    Thumbs up
    Carnak,I got it. Thanks a lot!!!!
    Apr 2002
    You're welcome
    How about Bathrooms?? - 8 ACH??
    I don't have Ashrae handbook
    Thank you.
    Talking
    Bath fans should be sized to provide the larger of 50 cfm or 8 ACH in the bathroom
    It depends on what mechanical code your under. IMC requires 75cfm's per fixture, there are also new requirements for shower heads as of the 2003 version. Always best to check with the local mechanical inspector. If its a new project or a re-hab there should be drawings approved by the local jurisdiction that will state what is required on all ventilation.
    Vern P: 2003 MBC,MRC,IFGC,IFC
    An HVAC-Talk Michigan Chapter Mechanical Inspector, Jurisdiction-Ann Arbor
    Smile
    thanks. I will check IMC.
    the section # is 403 the table giving the cfm's required per occupancy is 403.3