refrigeration having a rough need help
I change solenoid value on a water cool reach in freezer because the valve was leaking through .I also installed a delayed on break .That's all I did I vacuum the system then charge .From then I have been have problem with the .The suction goes to about 10 psi and the high side 310 .I check the strained on the Tx valve nothing works .
-
05-10-2011, 06:30 AM #2
Regular Guest
- Join Date
- Sep 2005
- Posts
- 7
Refrigerant is R 404 A.
-
05-10-2011, 06:59 AM #3
Is this hooked up to city or tower water?
Is this a Solenoid Valve or Regulating Valve?
What is the temperature of water in and out?
SH?
-
05-10-2011, 06:26 PM #4"The problem is the average person isn’t tuned in to lifelong learning, or going to seminars and so forth. If the information is not on television, and it’s not in the movies they watch, and it’s not in the few books that they buy, they don’t get it" - Jack Canfield