    Novar

    Heya Fellas
    Having a problem with my novar system
    Have a Novar I-Scope software/front end with a ESS-32 edit.
    Anywho I have a RTS-30 (Novar) temp sensor going into a IOM/2 Module and it is displaying -40 deg supply sensor, I changed the sensor and it says -40 deg supply sensor, I reversed the wiring and it gives OFAULT!
    So could I have a problem with my IOM/2 Module/Board, anyone know why?
    Thanks Guys
    Brian

    The signal is 4-20mA

  2. #2
    Quote Originally Posted by durussel78 View Post
    Heya Fellas
    Having a problem with my novar system
    Have a Novar I-Scope software/front end with a ESS-32 edit.
    Anywho I have a RTS-30 (Novar) temp sensor going into a IOM/2 Module and it is displaying -40 deg supply sensor, I changed the sensor and it says -40 deg supply sensor, I reversed the wiring and it gives OFAULT!
    So could I have a problem with my IOM/2 Module/Board, anyone know why?
    Thanks Guys
    Brian

    The signal is 4-20mA
    Try pulling the top section off and resetting

  3. #3
    Join Date
    Jan 2003
    Location
    USA
    Posts
    1,666
    Toss your meter on the current loop and see if it is what it should be.
    Propagating the formula. http://www.noagendashow.com/