    Honeywell T-Stat Spec Software

    I have a large project at Fort Leonard Wood involving Honeywell T7350A’s and T7350H’s. I have configured these with the T-Stat Spec software I downloaded off Honeywell’s website. My question is, when you are configuring the schedules, say if you have a building occupied Mon-Fri 0600-1730 with Sat and Sun un-occupied, do I leave Sat and Sun “un-configured”? Does the un-configured setting on those days make the space run off the un-occupied setpoints or is there a way to make those two days un-occupied all day without making them occupied for one minute a day then returning to un-occupied. I just don’t want the stat to go through optimal start/stop for 3 hours previous to a one minute occupied period during weekend days.

    This is a very large project involving hundreds of buildings, sold to the Gov't to conserve energy, so as much as I can conserve the better for them and me!
    When it is said that BacNet is a better protocol than LonWorks, I die a little more inside.
    ~knottyjabe

  2. #2
    Join Date
    Aug 2007
    Location
    Western Colorado
    Posts
    497
    I believe un-configured time slots will follow the mode of the last configured time slot.
    RealEyes
    Realize
    RealLies!




  3. #3
    Join Date
    Feb 2007
    Location
    Helena, Montana
    Posts
    2,129
    They don't have a base-wide EMCS?
    Don't worry zombies are looking for brains, you're safe...

  4. #4
    Loytec can do it.

  5. #5
    Join Date
    Aug 2007
    Location
    Western Colorado
    Posts
    497
    Third!
    RealEyes
    Realize
    RealLies!




  6. #6
    Join Date
    Dec 2010
    Location
    N 37° 10.573 W 093° 15.649
    Posts
    84
    I just got an anwser back from Honeywell and they said it will follow the current state until the next change of state, so weekends set for un-configured preceded by an un-occupied will remain un-occupied for the whole weekend. Thanx RAD1
    When it is said that BacNet is a better protocol than LonWorks, I die a little more inside.
    ~knottyjabe

  7. #7
    Join Date
    Dec 2010
    Location
    N 37° 10.573 W 093° 15.649
    Posts
    84
    Quote Originally Posted by ControlsInMT View Post
    They don't have a base-wide EMCS?
    That is what this project is...
    When it is said that BacNet is a better protocol than LonWorks, I die a little more inside.
    ~knottyjabe

  8. #8
    Join Date
    Feb 2007
    Location
    Helena, Montana
    Posts
    2,129
    Quote Originally Posted by knottyjabe View Post
    That is what this project is...
    Wow. There are a lot less expensive and flexible ways than using those, but if that's what's spec'd....
    Don't worry zombies are looking for brains, you're safe...

  9. #9
    Join Date
    Dec 2010
    Location
    N 37° 10.573 W 093° 15.649
    Posts
    84
    Yea, agreed, but you can't talk those people into anything different, like you said spec's spec!
    When it is said that BacNet is a better protocol than LonWorks, I die a little more inside.
    ~knottyjabe

  10. #10
    Join Date
    Dec 2010
    Location
    N 37° 10.573 W 093° 15.649
    Posts
    84
    Thanks to all for your help, my last issue with this is; if it is saturday(schedule is set as un-configured but in un-occupied, looking for a change of state on monday at 0600), and someone comes in to do some weekend work, and presses the "temporary occupied" button, the stat will go temp occupied for a set amount of time, when this override time expires does the stat go back to un-occupied or does it stop all control and wait for monday at 0600 when it will return to occupied mode?
    When it is said that BacNet is a better protocol than LonWorks, I die a little more inside.
    ~knottyjabe

  11. #11
    Join Date
    Feb 2007
    Location
    Helena, Montana
    Posts
    2,129
    I can't find anything that actually answers that. Logic would think it would go back to last known state, which would have been unocc, but I couldn't verify it.
    Don't worry zombies are looking for brains, you're safe...

  12. #12
    Join Date
    Aug 2007
    Location
    Western Colorado
    Posts
    497
    Covering ALL the bases aren't you knottyjabe? I don't blame you! I agree with ControlsInMt, don't know for sure in this instance but logic says...
    RealEyes
    Realize
    RealLies!




  13. #13
    Join Date
    Dec 2010
    Location
    N 37° 10.573 W 093° 15.649
    Posts
    84
    These questions are just paranoia, I have configured and installed these about 3 mos ago, and started thinking-hey, what if- I have had no complaints or issues but I also want them to be right, ya know. This project involves so many buildings, I just don't want to have to go back and alter configs on every building!
    When it is said that BacNet is a better protocol than LonWorks, I die a little more inside.
    ~knottyjabe

Page 1 of 2 12 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event