    Question

    Compressor not running in condensing unit. There is 24 and 208 volts to contactor. Compressor is not running. I checked the windings of the compressor and found that start to run has 5.6 ohms, Start to Run and Run to Common shows OL. Is it safe to say that the windings are bad in the compressor. The compressor was also very hot. This is a 15 year old coleman unit. I am new to the business and could use some help. Thanks

  2. #2
    Join Date
    Jan 2004
    Location
    Massachusetts
    Posts
    665
    Did you check the overload safety at the compressor? Is the contactor closed?
    "The value of quality is long rembered after the thrill of low price is forgotten."

  3. #3
    Join Date
    Jun 2003
    Location
    Jacksonville, FL.
    Posts
    4,313
    Sounds like the compressor is off on overload to me. Does it feel hot & does the condenser motor run?

  4. #4
    Join Date
    Jul 2005
    Posts
    32
    The compressor is off on internal overload.Take some cold water from your garden hose and run over the compressor until it resets the overload.Than run the unit you will probably find a low charge,or a stuck compressor.

  5. #5
    cool compressor and check capacitor, lra, charge, etc.,

  6. #6
    Join Date
    Dec 2004
    Posts
    3
    Originally posted by bradjmx4
    Did you check the overload safety at the compressor? Is the contactor closed?
    No i did not check the overload at the compressor. I will do this today. The contactor is closed. Thanks.

  7. #7
    Join Date
    Aug 2005
    Posts
    10

    compressor not running

    After cooling compressor, recheck windings, if you get a reading on all terminals, the compressor was out on overload. If this is true then you need to start compressor and check freon charge, a low charge will cause the compressor to heat up, since the freon in the system keeps the motor in the compressor cool. check for discolored wires on contactor and compressor, weak windings will cause overload and hard starting occurs which discolors or burns wires. a hard start kit could help.also check the contacts on the contactor to see if arcing has occured, blackening around contacts, you may need to replace the contactor. Just a few things to look at!

  8. #8
    Join Date
    Dec 2004
    Location
    Derby City
    Posts
    3,958
    nucareer: don't be offended, but what is your area of experience when it comes to HVAC. You sound reasonably knowledgable, but members of this site are usually very apprehensive about steering non-practioners into their equipment, for fear something may get damaged or worse, someone gets hurt.

    Please keep in mind also, that even though you may be more than capable of performing the tasks, checks, and tests referred to, this post is visible by ALL who visit. So someone that doesn't have your mechanical ability, tries to do-it-themselves and winds up electrocuting themselves. Not a very pleasant result.

    I caution my contemporaries in this sense, as we have had this dicussion in the past. Please use good judgement and caution when dispensing this type of advice. The best advice? DON'T!

    I advise you contact an HVAC professional and have the system checked.
    Everyone has a purpose in life..........even if it's to be a bad example.

    Seek first to understand, before seeking to be understood.

  9. #9
    Join Date
    Apr 2004
    Posts
    7,680
    Deleted, after reading mr Lloyds post.


  10. #10
    Join Date
    Dec 2002
    Location
    Toledo, Ohio, United States
    Posts
    12,901
    Good advice John, I saw your picture recently in the Great Lakes HVAC news.
    No Heat No Cool You need Action Fast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event