    Anyone have information on the Microzone CVV-90111-0-0-2 Controller? I have no literature for this controller and would like to at least know what terminals are for what.
    Jul 2001
    Canada
    Pretty straight forward
    Terminals are IDENTIFIED
    LEFT HAND SIDE low voltage input / output and ASD bus wiring
    Communication ASD- ASD +
    8 INPUTS ( IN )
    4 OUTPUTS ( AO )
    RIGHT HAND SIDE Power wiring and Pilot duty output wiring
    8 DIGITAL with NO / NC contacts ( DO )
    24 VOLT power
    The controller you are describing sounds like the Microzone II. Those terminals are clearly marked. This is an older Microzone unit. Possibly the Microzone I? It has a double terminal strip at the top and the bottom with mixed spade and screw connections.
    Apr 2003
    South Carolina
    that model number is for the legacy microzone1 generation it can be a water source heat pump,packaged rooftop or a satellite. What is it controlling? i can help with your question
    Yes! Any help will be appreciated. Its operating on a rooftop unit with vav controls with a 25 ton system. We just changed over one of the units from a 25 ton carrier and the other a 25 ton trane. Both are now Trane. A/C and economizer only. Heat is in the vav boxes. Thanks for your assistance!