    Anyone have information on the Microzone CVV-90111-0-0-2 Controller? I have no literature for this controller and would like to at least know what terminals are for what.

  2. #2
    Join Date
    Jul 2001
    Location
    Canada
    Posts
    1,913
    Post Likes
    Pretty straight forward

    Terminals are IDENTIFIED

    LEFT HAND SIDE low voltage input / output and ASD bus wiring

    Communication ASD- ASD +

    8 INPUTS ( IN )
    4 OUTPUTS ( AO )

    RIGHT HAND SIDE Power wiring and Pilot duty output wiring

    8 DIGITAL with NO / NC contacts ( DO )
    24 VOLT power


  3. #3
    Join Date
    Aug 2003
    Posts
    35
    Post Likes
    The controller you are describing sounds like the Microzone II. Those terminals are clearly marked. This is an older Microzone unit. Possibly the Microzone I? It has a double terminal strip at the top and the bottom with mixed spade and screw connections.

  4. #4
    Join Date
    Apr 2003
    Location
    South Carolina
    Posts
    82
    Post Likes
    that model number is for the legacy microzone1 generation it can be a water source heat pump,packaged rooftop or a satellite. What is it controlling? i can help with your question

  5. #5
    Join Date
    Aug 2003
    Posts
    35
    Post Likes
    Yes! Any help will be appreciated. Its operating on a rooftop unit with vav controls with a 25 ton system. We just changed over one of the units from a 25 ton carrier and the other a 25 ton trane. Both are now Trane. A/C and economizer only. Heat is in the vav boxes. Thanks for your assistance!