    Question on maintenance clean & checks

    We have recently change our procedure on our clean & checks (preventive maintenance visits). In the past we have always connected our gauges to evaluate the charge in the system, in doing so on occassion we have had situations arise where we may have caused a leak on schraders, valves, etc. going forward we now evaluate the system and perform industry/manufacture requirements such as checking static pressure, evaluating temps in return & supply to establish our splits, etc and only then if the system does not have good readings do we apply our gauges. keep in mind this procedure is only done on systems that we see once to twice a year. on tune-ups that we go on for the "first time" we more often apply our gauges.

    does anyone not recoomend this or are their companies out there that also operate along these same lines on their preventive maintenance?

    thanks for your input in advance!!

  2. #2
    Join Date
    May 2011
    Location
    Washington, DC
    Posts
    1,652
    Post Likes
    I disagree with this method. I also recently argued about this with my service manager. How do we know were not reading a 20 degree split because our coil is a frozen block of ice?! That may be a little exaggerated but my point to him and with this issue is you do not know what is happening on the refrigerant side of the system unless you put gauges on it and measure your superheat and subcooling. Is it metering properly? are we slugging the compressor? etc. You wouldn't be able to catch this on a preventative side unless you check whats is actually taking place inside the line set and coils. At least, that is my opinion.

  3. #3
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Strictly as a serviceman, I started doing that on some systems that were old, obviously no-one had been doing it before me. This in response to one system that you had to get your refrigerent wrench out to access the pressures and it wouldn't seal properly after I was done & the lady ended up buying a new system rather than pay for repairs. When I ran into such a system again I just explained the situation to the homeowner & let them make the decision. I used to use a chart that would tell me what my supply air should be based on dry & wet bulb temp with 400 cfm's being assumed.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  4. #4
    Join Date
    Mar 2011
    Location
    Utah
    Posts
    20
    Post Likes
    Thread Starter
    Ron & Tips, i appreciate the input very much and hope more will "chime" in. i want to make sure everyone understands that a very large majority of these systems are ones that we originally checked with gauges and got the proper amount of refrigerant in them to begin with...in fact most are systems we originally installed and we have been seeing them over and over for years. i do not have alot of service background and have takin over as service manager from the president of our company. i have heard his side of the theory and appreciate hearing others.

  5. #5
    Join Date
    Sep 2009
    Location
    Arnold mo
    Posts
    3,974
    Post Likes
    Quote Originally Posted by jasonTTT View Post
    Ron & Tips, i appreciate the input very much and hope more will "chime" in. i want to make sure everyone understands that a very large majority of these systems are ones that we originally checked with gauges and got the proper amount of refrigerant in them to begin with...in fact most are systems we originally installed and we have been seeing them over and over for years. i do not have alot of service background and have takin over as service manager from the president of our company. i have heard his side of the theory and appreciate hearing others.
    On most systems, I can't see why you wouldn't put your gauges on. I can't see where NOT putting them on benefits your company or your customers. Probably a more important concern is making sure the techs you are sending out know what the heck they are doing.
    An answer without a question is meaningless.
    Information without understanding is useless.
    You can lead a horse to water............
    http://www.mohomeenergyaudits.com

  6. #6
    Join Date
    Dec 2009
    Location
    Arkansas
    Posts
    76
    Post Likes
    We always put ours on.But carry a bunch of service port caps with new gaskets.We always replace the cap when we connect to a system, they are cheap and save a lot of call backs.On the service valves we always use leak loc when putting them back on.

  7. #7
    Join Date
    Jul 2006
    Posts
    1,091
    Post Likes
    New caps

  8. #8
    Join Date
    Jul 2002
    Location
    Yuma, AZ
    Posts
    2,755
    Post Likes
    Be a Pro...Check and record the data on the invoice.
    For maintenance use 2" hoses to the gauge with no manifold.
    For a cap, a metal 1/4" flare nut with a copper bonnet, wrench tight will seal well and discourages huffers.
    "I have never let my schooling interfere with my education."
    Mark Twain
    NEVER STOP LEARNING.

  9. #9
    Join Date
    Feb 2010
    Location
    Ontario Canada
    Posts
    1,341
    Post Likes
    Do you charge extra for the flare nuts and copper bonnets?

  10. #10
    Join Date
    Mar 2011
    Location
    Edna Bay, Alaska Highest concentration of black bears in the US
    Posts
    623
    Post Likes
    I aiways gauge up with my quick connect single gauges that I carry in my bag. Almost no loss. I don't use my manifold on a pm unless I need to adjust the charge.I also replace missing or damaged caps to cover my a$$.

  11. #11
    Join Date
    Jul 2010
    Location
    nebraska
    Posts
    2,810
    Post Likes
    I always hook up. Missing a crazy txv could well cost a compressor. Tell the techs to check if the schrader is leaking before they put the caps back on.

  12. #12
    Join Date
    May 2011
    Location
    Washington, DC
    Posts
    1,652
    Post Likes
    @Jason- Even though you may have seen these units over the years, that doesn't mean something hasn't changed since last year. Your there to do a PM, be professional and be thorough with your work, check your pressures, superheat and subcooling. The idea of not doing it is something that mostly comes from service managers who are "out of touch" with whats current in the field. The alleged fears range from cross contamination to losing refrigerant and leaking valves. All of which are simply addressed by having qualified techs doing the services and none of these issues should be a problem.

  13. #13
    Join Date
    Jan 2008
    Posts
    2,904
    Post Likes
    I see so many over-charged systems, I can't imagine NOT checking SH/SC.
    "Hey Lama, hey, how about a little something, you know, for the effort." And he says, "there won't be any money, but when you die, on your deathbed, you will receive total consciousness." So I got that goin' for me, which is nice. - Carl Spackler

  14. #14
    Join Date
    Mar 2011
    Location
    Jamestown,SC
    Posts
    45
    Post Likes

    always check pressure 1st

    I always check pressure 1st. Write them down, clean the coils then show the customer the difference after. Most of the time they are impressed and happy I took the time to explain it to them.

  15. #15
    Join Date
    Jan 2008
    Location
    athens, georgia
    Posts
    9
    Post Likes
    Typical p.m. call where I work consists of... check filter, if washable,wash, replace when needed... check coil for any debris, etc... check coil pan for standing water... vacuum drains from outside house,if pump is used, prime the pump a few times; add a pvc union if needed for easy coil access and cleanout...check capacitors for amp draw and mfg... clean coils when needed... check gauges for normalcy... get differential with a target of 18- 20... load up, move on

  16. #16
    Join Date
    Apr 2011
    Location
    Independence, MO.
    Posts
    142
    Post Likes
    i got in the habbit of hooking my gauges up first to ensure refrigerant is in the system. a few times i had cleaned the coil on a 2,3,4 year old system and then hook my gauges up to find no refrigerant.

    one time i did have to go back after a coworker serviced it due to no refrigerant. i almost left one with a leaky schader, but i got lucky and felt a breeze when a finger passed buy it. from then on i checked the schrader on every one. i would replace the questionable ones.

  17. #17
    Join Date
    Jan 2007
    Location
    N.E. Ok.
    Posts
    1,483
    Post Likes
    I don't have any problem running pm's for regular customers and not hooking up.
    No load indoor or out i don't see the benefit of artificially creating normal working conditions on equipment that i maintain and have a history with.
    I have a good professional working relationship with my regular customers.

  18. #18
    Join Date
    Mar 2010
    Location
    Houston
    Posts
    213
    Post Likes
    We avoid manifold hookup unless there is a suspected problem on annuals, especially if system is performing within airflow/pressure and temp/humidity specs after good visual and coils cleaned. This is especially true on new inverter/dc compressor r410a systems, but then again they talk to me pretty good about things that are hurting inside .



    K

  19. #19
    Join Date
    Jan 2002
    Location
    Ft.Worth,Tx
    Posts
    4,809
    Post Likes

    Cool

    Maintenance Requirement
    Filter
    Drains
    Blower
    Coil

    Check condenser Coil/airflow
    amp/motor
    contactor/ points
    run/cap value
    compressor amps
    LS-Pressure
    HS-Pressure

    SLT-superheat
    LLT-sub-cooling
    T.D. indoor
    humidity/ W.B.
    'Life begins with the journey each day'

  20. #20
    Join Date
    Mar 2011
    Location
    Utah
    Posts
    20
    Post Likes
    Thread Starter
    Thank you all for the great input, appreciate it very much!!

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •