    How do you loose efficiency of ac with dirty filter?
    If your filter is dirty it would make your blower motor pull less amperage. If your filter is dirty your pressures will be lower, will it loose efficiency because it doesn't have the same cooling capacity with a dirty filter?
    Houston,Tx.
    Well right off the top of my head for starters you will not be removing as much heat from your home with a dirty filter, and I think if I am not mistaken that is what an a/c is supposed to do remove heat.
    Jan 2003
    Kansas City
    You lose overall system capacity. A motor's amp draw is reduced with a dirty filter because it is moving less air. This decreases the load presented to the indoor coil. The coil ends up doing more latent heat removal and less sensible cooling. Unfortunately the shift is not equal.
    coggin air
    you are a professional member? Are you an hvac engineer?
    just wondering
    May 2005
    Western Kansas
    I once told a customer/buddy this after he asked a similar question and I changed his packed filter....."take a towel and duct tape it around your mouth and nose see how it's a little tougher to breath, then add another towel to simulate restriction..the same thing happens to your a/c and an unchanged filter, you're both starved for air"...btw, he takes much better care of his system since I talked to him in "laymans" terms. He's not a hillbilly nor stupid, just ignorant of how air conditioners work...it's amazing how many there are out there just like him...(they pay my bills, gotta love'em)
    Houston,Tx.
    Originally posted by ct2
    coggin air
    just wondering
    South Dakota
    Actually, as the filter gets dirtier there is something in the system that becomes MORE efficient. Do you know what it is?
    Yea the filter!
    May 2005
    well, lets see:
    a dirty filter restricts air flow. when the air slows down, more heat and water are removed. now, because the coil is designed to do X amount of heat at X cfm while running at a temp of X. you lower cfm, you lower demand on the coil and the coil will become colder. as it gets colder and colder, it removes more and more water. once the coil reaches about 32* F and below, you get:
    <for bigger pic click below>
    http://img242.imageshack.us/img242/5474/icee13qe.th.jpg
    May 2005
    THATS RIGHT! ICE. YOUR COIL FREEZES UP! HOME OWNERS:
    CHANGE THE D@MN FILTER!!!!!!!!!!!!!!!
    in a house, Appomattox, Va.
    With a well designed system you would be trying to hit the sweet spot where several performance curves hit their max. Airflow being off would shift you down the slope, so to speak.
    For cars a certain gear and speed will give best performance because the curves hit the optimun at a certain point.Hitting that area gives best mpg, even though the speed may be 35 mpg.
    blowers, compressors and othewr components have performance curves,too. An undercharge charge on a system by 5%, say, could increase capacity 8%, but power consumption 10%. There are figures out there for charges being off, can't recall the exact values, but txvs tolerate off charges better than fixed metering devices.
    Col 3:23
    May 2005
    BUT YOU STILL GET THE ICE!
    Yes because it loses cooling capacity.Take a look at the mfrs. detailed cooling capacity.Say a 3 ton with 1200 cfm and then with a 100 cfm,sensible is reduced.