Results 1 to 13 of 13
    Dec 2009
    Bristol NH
    half a frozen coil
    I have a 12.5 ton carrier roof top and the lower half of (circuit 1 ) of the evaporator freezes up. Poor temp drop good airflow pressure seem ok 8deg superheat on a low load. Plugged orifice?
    Quote Originally Posted by boilerman856 View Post
    It needs a technician. No DYI
    Good luck
    and the rest of the story is?
    give us something to work with
    Jan 2010
    boilerman856 looks like you have been a member for some time. Are you in the trade ?
    Dec 2009
    Bristol NH
    I am home now so by memory; 67f outdoor ambient, 34%rh, 77f eat cant remember wet bulb. 10 temp split. 150psi high side, 50psi suction.
    And it is only half of one circuit, stage 1.
    Dec 2009
    Bristol NH
    VTP99, yes i am in the trade but new to forums. Also I have very little experince with large commercial units like this.
    Jan 2010
    You should apply for pro. In the pro forums you will get all the help you need. Is the head pressure the same on both circuits ? Sorry i can not help you more because of the site rules.
    Dec 2009
    Bristol NH
    Yes the pressure in both circuits/stages is very close. I dropped the charge and wieghed in virgin 22. This unit is fairly old and looks like everyone has had a turn. How do I apply for pro? what is the difference?
    Jan 2010
    Get your post count to 15 and then apply. Trust me once your in you will come here all the time for good info.
    Dec 2009
    Bristol NH
    Thats what I thought about forums, but so far not much luck
    might want to take a peek at the drier
    Dec 2009
    Bristol NH
    Looks like the compressor and drier was replaced two years ago(aprox). should have swapped it when I recharged it, just ran out of time and thought I could get away with it...
    Jan 2010
    There are forums that you can't see as a regular member. Keep posting and apply asap.