Results 1 to 8 of 8
    Jul 2005
    Hmm
    I've installled a TXV (Sporlan CBBIVE-2-GA, exterbnally equalized) in the evaporator. The system seems to provide good cooling but after the system stops, the pressure in the lines does not equalize. As a result compressor cannot start again. It starts again only after resetting the changeover valve. I had to install a piston back temporarily.
    Is there something wrong in the way the TXV works?
    Or do just I need to add start assist to the compressor?
    The compressor is hermetic Copeland CR18KQ-PFV. TXV's equalizing tube was connected correctly and wasn't capped.
    Any help is appreciated.
    Thanks.
    txv's have to have a start kit. also you installed a txv that does not equilize (hard shutoff)
    Jul 2005
    If I install a hard start kit, wouldn't it be potentially damaging for a compressor to start against high pressure every time?
    no
    Fort Worth, TX
    Nope. A start capacitor gives the compressor the needed boost to overcome the static pressure on the piston head. There are hermetic pots out there that have had pot relays and start caps and have been humming along for years.
    Building Physics Rule #2:
    Building Physics Rule #3:
    Apr 2002
    Dallas, TX
    That is part of the reason why the TEV provides a higher SEER rating than a piston/restrictor.
    Since the pressures do not equalize, the compressor spends less time pulling suction pressures down upon start up. With a piston, the compressor must spend more time getting pressures to design conditions.
    Apr 2005
    NE PA
    I don't think this is true, since most new high SEER units use scrolls, which allow equalization when stopped.
    paul
    Apr 2002
    Dallas, TX
    If system pressures equalize during off-cycle, then the unit is less efficient than one which does not allow pressures to equalize. The SEER "D" test measures system efficiency when the unit is cycled on and off.
    Scroll compressors utilizing a discharge check valve should hold differential pressure, unless the check valve leaks. The check valve, as I recall, prevented the scroll compressor from "unwinding" during off-cycle which created a loud noise. I'm not sure if current scroll compressors utilize a discharge check valve.