    I am about to replace the furnace and the AC unite. The furnace is going to be 75,000 92% with seal combustion.
    The installer wants to install a 10 SEER condensing unite with model # HAC030AKC4 and a coil model # EDP30F19C2. Is this a good combiantion on a 2 1/2 tons unite. I am located
    in the chicagoland are. Thanks for your comments!!!
    Humberto
    Jan 2005
    Looks kosher to me.
    Both the coil and condenser models numbers indicate 30K btu.No problem.
    Apr 2003
    So, the furnace is a H9MPD075F12B (single stage)?
    I'd personally opt for a furnace upgrade to a 2-stage unit.
    The 10 seer is ok (the HAC is a good model), but the TXV coil EXD30F19C would be better for humidity control and efficiency.
    Have you had a 'load calc' done on your home?
    Nov 2001
    thanks for the comments,
    I would asked about upgrading to the TVX coil. He was the only installer who perform a J manual calculation and measure the size of the windows and amount of insulation in the attic.
    Thanks Guys!!!
    Apr 2003
    Sounds like you got a winner.
    Now just don't be surprised if he is a little higher than the other contractors.
    Quality workmanship is PRICELESS!
    Just checked yesterday and that is the exact same unit I have, however I have a 3 ton evap. I'm happy with the performance and cost of the system.