Results 1 to 11 of 11
    Jul 2005
    I just started up a new Rheem HP today and my suction pressure plummets to 0 within seconds. Head pressure 150, outdoor temp 100. All valves are open. Pressures won't equalize when I pull power. Any ideas?
    Do you see any frost forming on the liquid line or coils?
    Portage
    does this happen in both heat and ac mode?
    I don’t always drink beer, but when I do I prefer Dos-Equis. I am the most interesting man in the world. Stay thirsty my friends.
    Portage
    where in nc are you at??
    Mar 2002
    Richmond, Virginia
    Was indoor coil replaced also? Does it have a txv or piston metering device? If piston, it needs to be pulled and checked. Is it safe to assume that an external l.l. drier was installed and a micron vacuum achieved? Sounds like a restriction or a defective txv.
    There is nothing more frightful than ignorance in action....Mark Twain
    Jul 2005
    complete install. all old out and gone. new coil, lineset and all. Didnt try heat mode; no frost anywhere; I'm thinking TXV but scared to let it run long enough to really check it. Would the discharge be higher than 150 if TXV stuck closed?
    Mar 2002
    Richmond, Virginia
    I would switch into the heating cycle and compare the pressures on the liquid and vapor access valves at the o.d. unit. They should be very close to the same. Use the high side gauge only for this of course. If the pressures look normal I would look hard at the metering device at the indoor coil.
    Jul 2005
    thanks pro. Ill try that. Ive already got a coil on the way because I suspected the TXV. Need one shot one kill on this one. Lady is 76 and temps here are high. I didn't try adding freon. Whats the odds it was improperly charged at factory?
    Nov 2000
    Eastern PA
    Also check the location of the TXV sensing bulb. Many manufactures do not permanantly mount these bulbs where they will need to be for proper system operation due to installation issues in doing so. The sensing bulb may be keeping the TXV closed.
    ...seek, and ye shall find;..
    Ecclesiastes 10:2 NIV
    Jul 2005
    manufacturer sent new coil with TXV. fixed everything. happy customer, happy contractor!!
    Mar 2002
    Richmond, Virginia
    Good job!