    Fan running backwards

    I recall having a sympton like this. In my case the IFM run cap was bad. It seems the blade was occasionally spinning backwards due to the wind. Basically the fan ran in whatever direction it was spinning on a cool for cooling.

    It is possible the capacitor combination is misswired, leaving the 5 mfd out of the circuit.

    Good luck....

  2. #15
    Join Date
    Jun 2003
    Location
    Florida
    Posts
    9,481
    Post Likes
    If you're going back over take the correct capacitor with you......
    If everything was always done "by the book"....the book would never change.

  3. #16
    Join Date
    Sep 2004
    Posts
    3,142
    Post Likes
    beenthere
    Thanks , I thought that was the case

  4. #17
    Join Date
    Aug 2005
    Posts
    4
    Post Likes
    Thread Starter

    Fixed

    I went back today and got the right Capacitor, a 35/5 and did it right. Fan runs the right way and pressures are 70/225. It's cooling in the house and things are good. My partner is too big-headed to admit he crossed a wire. I think he had the fan and commom wires crossed, or maybe the fan wasn't getting the Capacitor, IDK.

    thanks for the tips, and some helpful answers.

    -Cal,
    Class of 2005, Dunwoody College of Technology, HVAC+R Systems Service

  5. #18
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,826
    Post Likes
    Cal,

    Nothing wrong with putting 2 caps together to get the required mfd.
    But, next time, use you cap meter to make sure your getting the required mfd, before you start the unit.

    Just a good double check, never know when you get a weak cap from factory.




    Ct2, no problem.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.