    Confused
    Greetings:
    I just purchased an anemometer so I can calculate flow into returns and out supplies to see if there are any serious duct leaks. Once I know the average velocity through the louvers, I need to plug in an area for the calculation.
    Seems to me there is a relatively constant factor, (perhaps mfgr. dependant) somewhere in the vicinity of .75-.81 to use, but I am not sure of:
    1. what factor to use?
    2. where to measure the louver: outside edges of frame, or inside where the louvers begin?
    Thanks.
    1.those numbers sound good...yes the manufacturer will be able to tell you the exact number.
    2.where the louvers begin(but I am guessing as to your meaning)
    try this measure the free area ,say 20 @1 inch x 5 inch areas in one grill...that would be 100 square inches
    there is an online catalog that should have them listed,if you know brand ,size ,item number
    You'll get close,if you are diligent,but there are better ways to do this.
    Apr 2002
    self edit
    http://www.ductstrap.com/
    Originally posted by Carnak
    self edit
    Interesting??
    SW FL
    Mfg Info
    All the manufacturers have on-line catalogs.
    See Ak
    For example,
    http://www.titus-hvac.com/ecatalog/
    http://www.metalaire.com/products_full_page.htm
    http://www.hartandcooley.com/grd/all_grd.htm
    __ Louvers, ?
    You mean Return Air registers and S.A. diffusers?
    Designer Dan
    Jul 2005
    Measuring Air Velocities Thru Louvers
    I would not recommend maesuring the air flow thru louvers. The way that the air flow enters or leaves a louver is hard to determine with a wind vane anemometer due to the erratic velocities. A hot wire anemometer would be better but you would need to take several readings to get a good average and record readings in places around the louvers that you may not realize.
    Both anemometers would be fine for diffuser or grille measurements as long as you follow the instruments instructions and get a true average.
    Most of the prominant manufactures list the "K"Factors for their products in the catalog or you can get some of them on the web.
    Remember to apply the correction factors for altitude if you are measureing air flows above 2000 feet above sea level. Some instruments require a temperature correction factor as well.
    Huntsville,AL
    plastic grills have much less free space!
    about 66% by my rough measuring, I changed back to metal!
    Central Kansas
    How about those decorative wooden grills?
    Nice to look at but I bet the net free area is less than 50%. The ones I have seen had no label or data regarding net free area. Greg
    Smile
    As usual, this forum provides fast and useful answers. To clear up the louver question, I should have more properly described them as return and supply registers.
    And thanks for the mfgr links... I have a mix of what looks like Hart & Cooley and a few replacements purchased at "The Depot" as the originals showed some rust.
    When we had our wood floor re-finished last year, we also had about six oak louvers installed and they look to be much more restrictive (less free area) than the metal. I guess the best thing to do is measure them directly.
    When I measured the airflow from the grills I was intending to take multiple measurements across the face and use the average to account for variations.
    Is there a proceedure for "balancing" the airflow as far as cfm's per room? Is it proportional to loads calculated by room in the manual J calculations, or it that over the edge a bit?
    Thanks again to everyone.
    Yes ,proprotional to the Man. J load for each room,based on total system cfm.
    You may need to lose the wood grilles.