Page 1 of 3 123 LastLast
Results 1 to 13 of 37

Thread: head scratcher

  1. #1
    Join Date
    Jul 2005
    Posts
    10
    Post Likes

    Hmm

    help install a 3 ton unit 87 degree outside which gave me my 265 lbs head pressure FLA 14.7 measure 13.5 inside temp 90 with dischage 71 got a call today she said by the therometers we left there for her to read room temp(which is by the return) 85 degrees discharge closes to the furance 68 degrees. Will be putting gauges on it when it stop raining here
    Goodman condenser unit with a Goodman 3ton a fram coil.
    Any idea buddy is at a lost and just left on vaction and drop it my lap. 1st year tech.

  2. #2
    Join Date
    Jul 2005
    Posts
    88
    Post Likes
    need more info. how big is house, subcooling, superheat, suction pressure, txv?,

  3. #3
    Join Date
    Jul 2005
    Posts
    88
    Post Likes
    Probably need to wait on buddy.

  4. #4
    Join Date
    Sep 2004
    Location
    Portage
    Posts
    915
    Post Likes

    Talking i agree with dexman

    lol
    I don’t always drink beer, but when I do I prefer Dos-Equis. I am the most interesting man in the world. Stay thirsty my friends.

  5. #5
    Join Date
    Mar 2005
    Location
    Serving Northern Va and surounding area
    Posts
    38
    Post Likes
    Please slow down and do SPELL CHECK !

    I JUST LEARNED HOW TO SPELL A/C TODAY

  6. #6
    Join Date
    Sep 2004
    Location
    Portage
    Posts
    915
    Post Likes

    not sure

    was that "tonto" or "jar-jar binks" ??
    I don’t always drink beer, but when I do I prefer Dos-Equis. I am the most interesting man in the world. Stay thirsty my friends.

  7. #7
    Join Date
    Dec 2004
    Posts
    201
    Post Likes
    he said it was a head scratcher

  8. #8
    Join Date
    Jul 2005
    Posts
    10
    Post Likes
    Thread Starter

    more imformation

    Ok sorry about the spell check thing being a tech noone is looking at your spelling just able to understande it. Well I just got a hold of my buddy and he thinks that it a bad compressor(compressor valves). The first day we install had 17 degree spread 90 degree room temp and a 73 degree discharge from the closes vent to the blower. She call the 2nd day being too hot still I check it out 15 deg spread 84 room temp 69 discharge today I went over 80 room temp 67 discharge which is 13 degree outside temp avg 95 deg. Suction pressure is between 80 to 72. Clean the blower and check the fan speed(which it was running on high). He will not be back off vaction until Saturday. I do not install these things all the time (1st year tech) how often these are bad from the start. How I got involve I work with this guy and he said want some extra cash help him with this job and if there trouble check it out now I feel responseable for it. He want me to pull out the old ref. vac. it out for a couple a hours then put fresh ref. just in some case that something got into the system. By that time he will be back and then if that does not work we will install a new condenser unit.

  9. #9
    Join Date
    Jan 2004
    Posts
    144
    Post Likes
    Sounds like Buddy needs to call a PRO...lol
    Licensing laws are tough, and it's about time.

  10. #10
    Join Date
    Apr 2003
    Posts
    6,383
    Post Likes

    Re: more imformation

    Originally posted by mtumeo
    how often these are bad from the start.
    Very unlikely!

    By that time he will be back and then if that does not work we will install a new condenser unit.
    How nice, install a new one... with no real facts as to why!?

  11. #11
    Join Date
    Feb 2003
    Location
    S.W. PA
    Posts
    3,298
    Post Likes

    Wow you are so far off I don’t know where to start

    You guys installed it how deep of a vacuum did you pull?

    What is your superheat?

    Pull out refrigerant and put new in just in case????
    Maybe bad compressor??????
    You are only measuring the "split" nothing else
    What did manual j say you needed??????
    How do you know the blower should be on high???
    Wtf like I said I don’t know where to start

    Man no offence but you guys need to stay away from this stuff until you learn how to do it

    And as far as a tech not needing to know how to spell well that’s just plain crazy
    Yes people do need to be able to make it out and I am not as good at spelling as I would like to be but there is spell check and dictionaries


    NOW DO NOT GO AND GET ALL PISSED OFF BECAUSE YOU ARE A HACK
    STICK AROUND AND LEARN THIS IS A GREAT PLACE TO DO IT

  12. #12
    Join Date
    Sep 2004
    Location
    Portage
    Posts
    915
    Post Likes

    Hmm ??

    "pull vac incase 'something' got into the system! like what? rabid bull elephant? please go to a local supply house and get some ref. books! information is a good thing, no need to be "askairt" of that book learnin
    I don’t always drink beer, but when I do I prefer Dos-Equis. I am the most interesting man in the world. Stay thirsty my friends.

  13. #13
    Join Date
    Mar 2005
    Location
    leland nc
    Posts
    4,526
    Post Likes
    first how do i use spell check on this dam thing
    next i completely agree with dhvac. you have already learn your first lesson side jobs if you cant fix it dont install it. make you look bad and everyone else in the trade to. stick arround you will learn a lot here and all these guy and girls will help you. leave the side jobs alone till you learn more you will be better off in the long run trust me on that. i learned it the hard way also

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.