    Economizer Troubleshooting

    Can anyone please tell me whats the proper procedure to troubleshoot the economizer module and the economizer actuator on Trane rtus with the relitel controller in them.

  2. #2
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    you got the black book?
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  3. #3
    what black book

  4. #4
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,705
    Google reliatel controls book
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  5. #5
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    I recently obtained the black book . . it will prove to be a valuable tool sooner or later

  6. #6
    Join Date
    Jan 2008
    Location
    Dallas ,Texas
    Posts
    3,705
    Really believe the white book is what he needs.
    UA 100

    It takes three people to do anything around here. Two do the work, one explains to the crowd of people who showed up when they seen smoke and flames.

  7. #7
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,088
    I have a red book
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  8. #8
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    which one is the white one ?

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,267
    The Black Book is Voyager Microcontrols. (UCP Board)

    The White Book is ReliaTel Microprocessor Controls.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  10. #10
    Join Date
    Oct 2004
    Location
    Central WA
    Posts
    1,490
    The white zone is for the immediate loading and unloading of passengers only. There is no parking in the red zone.

  11. #11
    Join Date
    Jul 2008
    Posts
    420
    Quote Originally Posted by bazylyzk88 View Post
    Can anyone please tell me whats the proper procedure to troubleshoot the economizer module and the economizer actuator on Trane rtus with the relitel controller in them.
    unsure what exactly your up against but in a nutsheel if the green light is on you have 24vac. The first thing i do is turn the minimium position setting to all the way open (CW) and see what happens. If OA damp opens id call the actuator itself good-look at economizer module and sensors. If there is no green light and you measure 24vac to T1 and TR1 on the econ module id call the module bad (the econ module sits right on top of the actuator and looks like its part of it.) Also take note of flashing green light on the econ module- steady on-conditions ok for free cool- slow flash-not ok for free cool. fast flash-no communication with refer board. Off agian is no power 24vac. Error codes are displayed as pulses 1/2 sec on, 1/4 sec off. 1 flash- actuator fault. 2-CO2 sensor, 3-RA humidity sensor. 4-RA temp sensor. 6 OA humidity sensor. 7 OA temp sensor. 8 MAT sensor. 9-11 flashes is internal fault. In my experiance communication failures is almost always the refer boards fault. I think you can also take the econ module off, jump 24vac from T1 and TR1 to the actuator and then close one of the other 2 inputs on the actuator and it should drive open if good. Hope any of that helpsw.
    "It's just like it doesn't work. I mean it seems to be ok now, but it usually like never works"

    "Never an always and always a maybe"

  12. #12
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Quote Originally Posted by timebuilder View Post
    The Black Book is Voyager Microcontrols. (UCP Board)

    The White Book is ReliaTel Microprocessor Controls.
    is manual RT-SVD03G-EN the white book ? how does one know when to use what? I'm just getting involved with trane units on a very frequent basis so am trying to find out any useful info lol

  13. #13
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,267
    Quote Originally Posted by hvac wiz 33 View Post
    is manual RT-SVD03G-EN the white book ? how does one know when to use what? I'm just getting involved with trane units on a very frequent basis so am trying to find out any useful info lol
    The older units (typically a Voyager) have a very large processor board, called the UCP board. The lower left hand corner has a red LED. If you want to use a conventional thermostat (as opposed to a Trane thermostat) you would get a second "interface" board (CTI) that provides for a conventional thermostat. This type of unit requires the black book. Pub 22-7706-06.

    The newer units (such as the Precedent) use a much smaller ReliaTel board, with a green LED, and the ability to directly connect a conventional thermostat to a terminal strip along one side. This would use the newer "white" book. The one I have is No. RT-SVD03D-EN.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event