    First post here - great forum, thanks to all you pros/experts helping out!

    I bought this 1946 home a few years ago, my first home. It has no A/C because as folks in the SF bay area know - you don't need A/C here (HAH!). My first summer it was over 90F in my house for a couple of days and I decided A/C is critical (I'm from Miami where A/C = life). I ended up replacing the 20yr furnace with a complete 4 Ton Trane 14XLi setup reusing my existing ducts etc but adding a return and one vent in the kitchen (which had none). I have a lot of complaints and problems but I'll save the rant for anyone who wants to pull it out of me. What I'm hoping for is help addressing my electric bill, which is HUGE, and a warm-room cold-room issue, and about 17 times less important is the ridiculous amount of wind-noise coming out of my (newly installed) kitchen A/C vent which is very close to the assembly in the attic.

    The state of things. I have plenty of windows on my southern exposure - all are reasonably new double-paned gas filled UV tinted windows (some framed in aluminum, some in plastic). Most of the house has an attic. Most of the vents are flexible insulated and hanging from the roof, some are bent hard enough that I wonder if the duct inside the insulation is somewhat blocked form being bent constrained. From the attic I can see the shake-shingles and the roofing nails etc. There is about 2" of blown-insulation scattered around the attic floor. The largest room, a recentish addition, has no attic and a high ceiling - this room has two 10 or 12" square vents with huge ducts connected to them (they are both vents, not returns) - this room is always the coldest in the house. The master BR runs hot in the summer and the study (on the north-west corner of the house) runs way hot in summer and way cold in winter. I have tall trees on the east side of my home and get very little sun from there, moderate sun from the south, and the NW corner gets a lot of sun in the late afternoon. The master BR has two tiny vents (4" ducts) and the study (NW) has a single small vent (4" duct); the study is almost directly below the attic-unit.

    I hope I provided enough, and not to much info. I'm happy to crawl/measure/smell to get more data if that helps.

    Thanks in advance for any advice you would offer.



  2. #2
    Join Date
    Jul 2005
    Posts
    8
    Post Likes
    Thread Starter

    old house, new AC, frustrated HO

    oh yeah - 2000 sq ft house.

  3. #3
    Join Date
    Jul 2002
    Posts
    962
    Post Likes
    I don't beleive you can evaluate your problem Accurately over the internet. There are so many things to concider. I would want to make sure the new A/C is installed properly and all readings normal before I dove into such a situation you describe. Old houses where only sized for heating. So I suspect this could be some of your problem, but there are a few tests that should be run.

    What did the installing company have to say?

  4. #4
    Join Date
    Jul 2005
    Posts
    8
    Post Likes
    Thread Starter
    I should point out that the system cools my house quickly and as cold as I want and is as effective at heating (though neither evenly), I want to get it working more energy efficiently and more balanced across rooms. After a few hours of reading related threads on this site I realize I am a long long ways away from figuring this out myself while I'm not looking for a change in trade.

    I haven't contacted my HVAC installer because they screwed up the initial install (oil and water leak - half the ceiling replaced after weeks of complaining) and the repair work they did on that original install left something to be desired (water leak resulting in replacement of the same 1/2 ceiling again the following summer). I got a referral from Home Depot to a local company that's been in business near me for decades (not sure if the forum rules allow bad-naming so you can ask me and I'll tell you). They were easy on the way into my wallet but poor once they got in. I think they way oversold me and failed to give me appropriate guidance. Which brings me to why I'm here - plenty of folks who seem reasonable.

    Given the long list of typical shortcomings in my system I'm hoping to get guidance on what are the ones that will get me most bang for my time and money - that may very well be unreasonable to answer remotely in which case I will need to find someone else locally.


  5. #5
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes

    Generally speaking, the contractors who subcontract work from Homedepot, Sears and the like are those who agreed to perform the work at the very lowest prices so Homedepot and Sears could make the profit. You can be sure that even if you think Homedepot just made a referral that money was probably exchanged between them or they have an agreement. Those agreements are always in favor of the chain not the smaller contractor. Therefore, the contractor has to be in and out of the job as fast as possible or they don't make money.

    Higher quality contractors don't work for the Big chain stores. I doubt that you will get any satification from your current contractor. I would not want them back after the mess they already made.

    So, you are probably in a situtation where you are going to have to pay twice and hire a quality contractor. Don't be suprised to learn that there are more things that were not done correctly or short-cuts that were taken when the new contractor has a look at the installation.


  6. #6
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    first, add more insulation into the attic!!

    sounds like you have basic house construction issues, as well as no ducting design --

    you spent big $$ because of 2 days of 90F?

    probably big bills are due to lack of insulation, lots of infiltration, oversized unit, poor ductwork which is probably leaking, lack of shade -- alum window frames = alum is an excellent conductor of heat or electricity.


  7. #7
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes

    I am sure they did a Manual J heat load calculation, right? If they did they would have caught the building construction issues if they exist.

    Then using the information from the Manual J calculation they calculated the duct sizes as well, right?

    Doubt it!


  8. #8
    Join Date
    Jul 2005
    Posts
    8
    Post Likes
    Thread Starter
    cem-bsee,
    >first, add more insulation into the attic!!

    Am I better off putting the insulation under the roof or ontop of the ceiling. I the roof is shake and I can see the bottom of the shake from the attic.

    >you spent big $$ because of 2 days of 90F?
    I had been living in the area for a few years and saw how poorly my home handled a warm day and decided that AC is a requirement here as it is in my home town. In wasn't clear in my previous posts but that was not a particularly hot day for the area and the temp. in my home was way higher than outside; there are three or so months a year where the daily high is in the 90s and that would've made the inside of my home 100+. I think I could've probably gotten a smaller system and spent the difference on overall quality (duct upgrades, insulation improvements, ...). I thought I chose a quality firm as they had long standing and bid right in the middle of the five bids I got.

    NormChris
    > I am sure they did a Manual J heat load calculation, right?



    As you guessed they filled out an order form based on sqare footage and scheduled an installation, that was the end of that. I should've done as much research on the craft as I did on the price.

  9. #9
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes

    Did they get a permit and have an inspection?

  10. #10
    Join Date
    Jul 2005
    Posts
    8
    Post Likes
    Thread Starter
    NormChris
    >Did they get a permit and have an inspection?
    Yep though the inspector only looked at the unit outside the house, he never came in side - I got the permit closed. Permit is listed for "replace furnace and install A/C."

  11. #11
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes


    So the inspector never went inside to look at the new furnace that was replaced? Really?

    What city in the San Francisco area do you live in? I lived in San Jose for 25-years.


  12. #12
    Join Date
    Sep 2002
    Location
    South Dakota
    Posts
    6,580
    Post Likes

    Perhaps the inspector is afraid Homedepot will take away his discount card. I actually saw that happen years ago with Montgomery Wards.


  13. #13
    Join Date
    Aug 2003
    Location
    Central Kentucky
    Posts
    6,258
    Post Likes
    happygolucky,check out http://www.nationalcomfortinstitute.com & do a contractor search.

    The contractors who have recieved this training in your area specialize in correcting problems like yours.

    Good Luck
    Have you set up a Google alert for Carbon Monoxide yet?
    Click here to find out how.

  14. #14
    Join Date
    Oct 2002
    Posts
    70
    Post Likes
    First of All:

    HomeDepot allows the contractor to provide man power for the 10 SqFt of space in the building. For this the contractor has the right to sell you an air conditioner and furnace. Now the contractor is responsible to man the store at a minimum of 40 hours per week. The contractor pays this person $10.00 per hour (Called a LEAD Generator) to talk you into allowing their salesman to come to your home for an estimate. Now the salesman depending on the company earns from 8% to 10% for making the sale. The contractor pays the salesman this commission and then pays HomeDepot 10% for this wonderful opportunity to do a lousy overpriced installation for you. Now the contractor has to make a profit on top of all of these other costs. What part of you have been had don't you understand???????????

    Second: You have a very difficult installation due to the age and construction of your home. You absolutely need to have a contractor that has some idea of heat loss / heat gain calculations, proper duct sizing and how to install it correctly.

    Third: It sounds as though your insulation is well below reasonable standards complicating your comfort problems and operating expenses.

    Good Luck, you have been had!!!!!!!!!!!!!!!!!

  15. #15
    Join Date
    Dec 2004
    Location
    Derby City
    Posts
    4,120
    Post Likes
    Originally posted by NormChris

    Generally speaking, the contractors who subcontract work from Homedepot, Sears and the like are those who agreed to perform the work at the very lowest prices so Homedepot and Sears could make the profit. You can be sure that even if you think Homedepot just made a referral that money was probably exchanged between them or they have an agreement. Those agreements are always in favor of the chain not the smaller contractor. Therefore, the contractor has to be in and out of the job as fast as possible or they don't make money.

    Higher quality contractors don't work for the Big chain stores. I doubt that you will get any satification from your current contractor. I would not want them back after the mess they already made.

    So, you are probably in a situtation where you are going to have to pay twice and hire a quality contractor. Don't be suprised to learn that there are more things that were not done correctly or short-cuts that were taken when the new contractor has a look at the installation.

    Norm, not making fun, now, but I gotta tell you I REALLY like the word used above: "satification." Even if it isn't, it ought to be a REAL word. Definition: being able to provide justification for the feeling that one has been satisfied. I LIKE IT! LOL
    Everyone has a purpose in life..........even if it's to be a bad example.

    Seek first to understand, before seeking to be understood.

  16. #16
    Join Date
    Jul 2005
    Posts
    8
    Post Likes
    Thread Starter
    NormChris
    >So the inspector never went inside to look at the new furnace >that was replaced? Really?
    >
    >What city in the San Francisco area do you live in? I lived >in San Jose for 25-years.
    Los Altos.

  17. #17
    Join Date
    Jul 2005
    Posts
    8
    Post Likes
    Thread Starter
    crt,
    >Good Luck, you have been had!!!!!!!!!!!!!!!!!
    If I've really been had than I could try to get a partial refund out of them, whereas if I just got a cruddy job then 'buyer beware' is probably the rule and I'll have no real recourse. Have I been mistreated or genuinely screwed?


    All,
    Thanks for your help. Barring the belief that I should go after these guys for some of my money back I'm hoping to address this myself if possible. I spent the day addressing door insulation and holes between the interior and attic including a 1' x 4" gap between my bathroom exhaust fan body and the ceiling-board/cross-members (my shower no longer fogs the mirrors where before it was over a foot of fog).

    The consensus seems to be that I should address attic insulation next; should I be looking at the underside of the roof, or, the attic floor?

    thanks much

  18. #18
    Join Date
    Jul 2005
    Posts
    45
    Post Likes
    The consensus seems to be that I should address attic insulation next; should I be looking at the underside of the roof, or, the attic floor?



    Definitly the attic floor. Also make sure that your ducting is insulated. Don't know about the west coast, but here in the south east old heat only systems did not require duct insulation. Therefore, whenever we add a/c to a house, we either insulate or replace the ductwork.


    good luck!!



    [Edited by theredneckrev on 07-31-2005 at 03:32 PM]

  19. #19
    Join Date
    Feb 2005
    Location
    Dothan, Al
    Posts
    3,461
    Post Likes
    To me the size of system is not a problem.
    Operation of system may be.
    Sounds to me like ductwork problem.
    Have new contractor determine ductwork possibilities.
    And as others have said, insulate.

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •