Results 1 to 7 of 7
    Apr 2005
    Fredericton NB
    We have some Honeywell BNA's on three XL Plus buses and 3 Xl 5000 buses. Is there any thing available to protect the BNA's from lightning on the bus. We recently had a lightning storm that took out comm chips on some xl plus panels and wiped out one of the BNA's.
    Jan 2002
    New Hampshire
    rotsa ruck
    I worked on a campus on top of a hill with that system.
    After enough lightning storms, the copper conductor phone lines between the buildings were all replaced with fiber optic cables.
    Now they only lose one building at a time.
    Noel
    Indianapolis
    At one point 3-4 years ago, Honeywell had a lightning arrestor that you could install on the bus. I had 2 buildings connected by a parking garage that seemed to attract lightning. Put one at each building where the bus entered and haven't lost a chip since. Not sure what the part number is though.
    Manchester NH
    Exclamation Fiber
    Noel,
    You know they have not installed the fiber and they do not have xlp panels. They have used a lightning device made by Transector. But you are correct that fiber is the way to go. They could go with a RS485 x filer converter.
    Huntsville,AL
    be sure that the elec power system is well grounded, likewise for the panels involved!
    SE Penna.
    Honeywell has a series of lightning supression devices available. Part numbers are as follows:
    14502412-008 Totalizer (high frequency digital inputs)
    14502412-011 120 VAC power
    14502412-012 C-Bus communication
    14502412-013 240 VAC power
    14502412-014 Analog inputs
    They are all still available from Honeywell.
    Apr 2005
    Fredericton NB
    xl plus lightning
    Thanks for all of the replies they are very helpful.