    3 phase compressor ohm readings
    what is the cause or affect of a 3 phase compressor having diffrent ohm readings
    Mar 2011
    Nw.Connecticut
    How different less than .5 ohm ?
    Apr 2011
    Nashville,TN
    are you sure your ohming it correctly? a single phase will ohm out maybe like
    c-r=2
    c-s=6
    s-r=8
    but on a 3 phase example
    c-r=2
    c-s=2
    s-r=2
    make sure you turn off the power and pull of the wires!!
    Apr 2011
    Nova Scotia Canada
    yes, I checked it correctly. All wires off and no power. I don't remember the exact ohm readings but one was something crazy like 0 ohms then 14ohms and 24 ohms if I remember correctly.I have never seen this before.I compared this to identicle compressors on the rack and they all checked out o.k.When the comp. is started it trips the breaker immediately.I also cheched to ground.
    Dec 2008
    Ontario Canada
    if all wires were disconnected at the compressor and those measurements were taken at the bare terminals, then it sounds like you got it, bad compressor, they don't usually fail like that your right to be suspicious and double check
    voltage imbalance?
    bad contactor? (single phasing)
    Jan 2010
    Sounds like one winding is open to me.
    Apr 2011
    you need a new compresser.they sould all ohm the same