Master reset on a Honeywell webstat
We recently installed and configured a honeywell webstat which was working perfectly and could be accessed without issues on the LAN side. The customers' IT department was trying to get access to it over the WAN and ran into issues. In one of their attempts to figure it out, we think that they may have changed the ip address or subnet mask and now were completely locked out of the WebStat.
Is there a way to do a master reset on the webstat without using the serial system shell? we don't have a computer available with a RS-232 port.
Thanks,
-
04-27-2011, 04:44 PM #2
all i can find is a password reset, not a system restore, so to speak...
Better to die standing, than to live on your knees.
~ Ernesto "Che" Guevara
-
04-27-2011, 05:24 PM #3
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
If it uses a static IP address, then when it is running it will send out messages from its static address.
So plug it into a hub (not a router) and plug your computer into the hub as well. Launch wireshark, power up the router and read its IP address from the packets it sends.
-
04-28-2011, 11:55 AM #4
Regular Guest
- Join Date
- Apr 2011
- Location
- Northern NJ
- Posts
- 11
Thanks BACnet. I'll try that.
-
04-28-2011, 12:14 PM #5
Regular Guest
- Join Date
- May 2008
- Location
- north east PA
- Posts
- 46
-
04-28-2011, 12:38 PM #6
Regular Guest
- Join Date
- May 2008
- Location
- north east PA
- Posts
- 46
bacnets idea w
ill not work
-
04-28-2011, 12:49 PM #7
BACnet knows what he's talking about, TCP/IP basics.
The WEBstat is a JACE-2, so yes, a null modem cable and hyperterminal will get you serial shell access where you can reset all of your IP settings.
In order to FTP in, you need a couple of things: a) the service must be enabled, b) you need to know the ip address.
FTP is for transferring files, not restarting the platform. That's done on another port entirely (default 3011).
The issue here is that the ip and/or subnet mask were changed, so he can't get in at the previously known ip.
Another utility that has been talked about numerous time here is Colasoft's MAC scanner.
-
04-28-2011, 03:22 PM #8
Regular Guest
- Join Date
- Apr 2011
- Location
- Northern NJ
- Posts
- 11
I used an available computer with a RS-232 port and was able to get serial shell access to the WEBstat. During the boot sequence the TCP/IP network status was displayed and the netmask was displayed as 0xc0a80101 which is translated into 192.168.1.1. So it seems that they entered the Gateway address as the Subnet mask.
Now the problem i've ran into is I cant login into the system shell menu using the default login in credentials to change it. Does anyone know the which credentials it's looking for? The default Username SysAdmin and Password !Sys!Admin arent working.
Thanks for all your help so far.
-
04-28-2011, 03:42 PM #9
During boot up while in serial shell access mode there should be a prompt to reset the platform credentials to the factory default. I'm assuming you set the jumper for serial shell access.
-
04-28-2011, 03:43 PM #10
Removed by Admin- No Return
- Join Date
- Aug 2009
- Posts
- 2,459
Ouch, that's quite a pickle!
I didn't know that they allowed netmask fields to take values other than 0 or 255. That last "1" is painful.
-
04-28-2011, 03:48 PM #11
-
04-28-2011, 03:52 PM #12
Regular Guest
- Join Date
- Apr 2011
- Location
- Northern NJ
- Posts
- 11
I saw the prompt to reset the credentials to the factory default, but i still dont know what the default credentials are. They were never changed on the initial setup. I also tried tridium and niagara. didnt work either.
I didn't think so either. You cant even change the mask those incorrect values in the TCP/IP settings on the PC.
-
04-28-2011, 04:04 PM #13