We aren't talking about pumping a scroll into a vacuum. Not in that way.
Chuck, I know what your saying, but my only concern is with the customer. You can't tell me that needle hasn't dropped like a rock on you before. It's done it to me. On something as much of a crapfest of a happy customer as a warranty replacement coil (which btw, we are starting are rounds again....*sigh*), why take the chance? We usually just close it off, recover, repair, pump, recharge (virgin)."Better tell the sandman to stay away, because we're gonna be workin on this one all night."
"Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."
"Just get it done son."
Dad adjusted
-
04-27-2011, 09:53 PM #29
TXV, he added refrigerant thinking it was low most likely but the pressures never changed. Since they didn't TXV. just let them change it a TXV is a simple device that can go bad easily.
-
04-27-2011, 11:17 PM #30
-
04-27-2011, 11:35 PM #31
-
04-28-2011, 12:48 AM #32
The problem is that some of the theory presented is wrong. We hear things like "SH and SC tell you where the refrigerant is in the system.". Well that's a nice thought. It is however a misguided thought. With a complete restriction at the MD all of the refrigerant gets trapped in the condenser and LL. Nevertheless the SC will stabilize at exactly 0.
-
04-28-2011, 09:59 AM #33
Yes, my statement was based on the assumption that correct refrigeration theory was being taught. Regardless the point you raise is a good one. I would rather say "Superheat and subcooling tell you what is going on in the evaporator and condenser" vs. "SH and SC tell you where the refrigerant is in the system". The refrigerant is everywhere in the system! It's undergoing changes throughout the entire system! It's up to the tech to know what these changes signify, and whether such changes are normal or not.
With a restricted metering device, there is little heat load picked up in the evaporator entering the condenser to be rejected. Head pressure falls due to lack of heat load. Pressure and temperature are relative; if the temperature via heat load is reduced, so will the pressure be reduced. And with that the saturated condensing temp approach to outdoor ambient temp (the basis for subcooling). Liquid stacks in the condenser, reducing the amount of coil that can actually condense superheated vapor from the compressor back to a liquid. If the vapor is able to condense at temperatures near outdoor ambient temp, there won't be much subcooling."In this house we obey the laws of thermodynamics!"
- Homer Simpson
-
04-28-2011, 10:16 AM #34"Everyday above ground, is a good day".
"But everyday that you have made a difference in someones life, may insure you stay above ground a little longer".<aircooled>
-
01-17-2012, 08:40 AM #35
Skilowyo,