Thread: carrier won't cool Tech wants to replace TXV

  1. #21
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    For those of us techs who have had a TXV fail on us, but our initial reaction was to think the system was low on charge, I will maintain that your initial tech was correct on the TXV failure (as evidenced by the new tech replacing it and you have cooling again). The thing I have to remind myself as a tech is that my first response when I find a system with what appears to be a low charge, don't add any refrigerant until any other factor that can contribute to the same symptoms has been found and eliminated. Just the other day I had a rooftop unit that indeed was low on charge. I started to add gas but stopped myself. Partly because my eyes zoomed right in on where the leak was. I could see it even without breaking out leak detector. Partly because even if the leak had not been that obvious, it was foolish for me to keep adding gas to a system with no other factors causing it to indicate a low charge but a low charge itself, which can only be due to a leak.

    Old habits are hard to break. Knee jerk reactions in service aren't always the best.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  2. #22
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Glad to hear they've got it working.

    I agree with shophound. Sounds like he figured on bad txv, which it was. I've had txv's bad out of the box, and I've had txv's go bad after a week.

    Kevin, I'm not arguing, but:
    IF you thought there was the possibility of a loss of charge, why would you pump a unit back into itself? Your not worried about sucking moisture in, especially with a possible malfunctioning txv?
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  3. #23
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    if a system is properly charged on start up and then the txv fails you have high sub cool and high superheat if he added refrigerant to get the proper sub cool then either the unit was not charged correctly on start up or the refrigerant leaked out.if the tech that replaced the txv followed proper procedures then the system should leak free

  4. #24
    Join Date
    Feb 2010
    Location
    A Noisy Compressor Room
    Posts
    8,263
    Post Likes
    Quote Originally Posted by hvacvegas View Post
    Glad to hear they've got it working.

    I agree with shophound. Sounds like he figured on bad txv, which it was. I've had txv's bad out of the box, and I've had txv's go bad after a week.

    Kevin, I'm not arguing, but:
    IF you thought there was the possibility of a loss of charge, why would you pump a unit back into itself? Your not worried about sucking moisture in, especially with a possible malfunctioning txv?
    If you don't let it pump down into a vacuum you can't suck any moisture into it. I usually just get it down to 5 psi and shut it off.

  5. #25
    Join Date
    Mar 2011
    Location
    Galveston Texas
    Posts
    530
    Post Likes
    In all reality your not suppose to pump a scroll compressor into a vacum state anyway

  6. #26
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    Quote Originally Posted by curtbsa View Post
    A new tech came out. Said first tech had added refrigerant to do diagnostics. He replaced TXV, emptied system and refilled. Said should be good to go. Did not give me new pressure readings though.that doesn't say much for the "tech" Seems to be cooling now. I'll be back if any more problems. Thanks again.
    you should ask his boss for those numbers

    saying it is charged correctly and not documenting it is the same as a lie in my book
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  7. #27
    Join Date
    Dec 2008
    Location
    Ontario Canada
    Posts
    758
    Post Likes
    Quote Originally Posted by cuchulain View Post
    In all reality your not suppose to pump a scroll compressor into a vacum state anyway
    they say not below 25psi, not enough oil pressure to maintain that thin film between the scrolls, and they start scraping against each other

  8. #28
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by cuchulain View Post
    In all reality your not suppose to pump a scroll compressor into a vacum state anyway
    We aren't talking about pumping a scroll into a vacuum. Not in that way.

    Chuck, I know what your saying, but my only concern is with the customer. You can't tell me that needle hasn't dropped like a rock on you before. It's done it to me. On something as much of a crapfest of a happy customer as a warranty replacement coil (which btw, we are starting are rounds again....*sigh*), why take the chance? We usually just close it off, recover, repair, pump, recharge (virgin).
    "Better tell the sandman to stay away, because we're gonna be workin on this one all night."

    "Dude, you need more than 2 wires to a condenser to run a 2 stage heatpump."

    "Just get it done son."

    Dad adjusted

  9. #29
    Join Date
    Jul 2010
    Location
    North Carolina
    Posts
    119
    Post Likes
    TXV, he added refrigerant thinking it was low most likely but the pressures never changed. Since they didn't TXV. just let them change it a TXV is a simple device that can go bad easily.

  10. #30
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by catmanacman View Post
    if a system is properly charged on start up and then the txv fails you have high sub cool and high superheat if he added refrigerant to get the proper sub cool then either the unit was not charged correctly on start up or the refrigerant leaked out.if the tech that replaced the txv followed proper procedures then the system should leak free
    A restriction at or within the metering device will cause a drop in SC.

  11. #31
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    A restriction at or within the metering device will cause a drop in SC.
    Thank you! I was gonna say the same but you beat me to it.

    Hey folks, if you ever hear anyone dissing "all that refrigeration theory crap", tell them to take a long walk off a short pier.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  12. #32
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by shophound View Post
    Thank you! I was gonna say the same but you beat me to it.

    Hey folks, if you ever hear anyone dissing "all that refrigeration theory crap", tell them to take a long walk off a short pier.
    The problem is that some of the theory presented is wrong. We hear things like "SH and SC tell you where the refrigerant is in the system.". Well that's a nice thought. It is however a misguided thought. With a complete restriction at the MD all of the refrigerant gets trapped in the condenser and LL. Nevertheless the SC will stabilize at exactly 0.

  13. #33
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    The problem is that some of the theory presented is wrong. We hear things like "SH and SC tell you where the refrigerant is in the system.". Well that's a nice thought. It is however a misguided thought. With a complete restriction at the MD all of the refrigerant gets trapped in the condenser and LL. Nevertheless the SC will stabilize at exactly 0.
    Yes, my statement was based on the assumption that correct refrigeration theory was being taught. Regardless the point you raise is a good one. I would rather say "Superheat and subcooling tell you what is going on in the evaporator and condenser" vs. "SH and SC tell you where the refrigerant is in the system". The refrigerant is everywhere in the system! It's undergoing changes throughout the entire system! It's up to the tech to know what these changes signify, and whether such changes are normal or not.

    With a restricted metering device, there is little heat load picked up in the evaporator entering the condenser to be rejected. Head pressure falls due to lack of heat load. Pressure and temperature are relative; if the temperature via heat load is reduced, so will the pressure be reduced. And with that the saturated condensing temp approach to outdoor ambient temp (the basis for subcooling). Liquid stacks in the condenser, reducing the amount of coil that can actually condense superheated vapor from the compressor back to a liquid. If the vapor is able to condense at temperatures near outdoor ambient temp, there won't be much subcooling.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  14. #34
    Join Date
    Jan 2002
    Location
    Ft.Worth,Tx
    Posts
    4,809
    Post Likes
    Quote Originally Posted by curtbsa View Post
    I really appreciate all the replies. A new tech came out. Said first tech had added refrigerant to do diagnostics. He replaced HVX, emptied system and refilled. Said should be good to go. Did not give me new pressure readings though. Seems to be cooling now. I'll be back if any more problems. Thanks again.
    I would ask what the pressure where /temps and T.D. after charge. You are owner of system..Required info..
    'Life begins with the journey each day'

  15. #35
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Skilowyo,


    Please start a new thread if you need help.



  16. #36
    Join Date
    Jan 2010
    Location
    North Huntingdon,Pa
    Posts
    358
    Post Likes
    Quote Originally Posted by rselby View Post
    What was the ambient temperature? He didn't calculate superheat, which would have been really nice to know. Shooting from the hip, yes you have a leak and a 7* split (with missing information) could be a TXV, but I'd need more info to be exact.
    He should have noted superheat,on a fixed txv,mfgs wants 10-11 degrees subcooling,the superheat is what it is at that designed subcooling number.
    PA#9377
    Your Satisfaction...Our Goal.

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •