Results 1 to 13 of 31
    Jul 2005
    I am having a new 5 ton 14 SEER AC being installed today in a 2500sqft home. There is a single return air sized at 20" x 25". Is this big enough? I've heard 100sq" per ton and 200sq" per ton. Which is correct?
    Robert
    Feb 2005
    Is it a stamped face return grille? Or a filter grille?
    Sounds like even if it is a stamped face grille it is more than a ton undersized....
    Jan 2002
    Ft.Worth,Tx
    Robert
    It really depends on the size of the ductwork attached to opening.
    But, if your using rule of thumb method 144 sq.in. per ton or 24x6-x5 will give you a close estimate.
    'Life begins with the journey each day'
    Jun 2002
    A single return results in poorly balanced airflow. They can also be noisy.
    IMHO, you should have a return in almost every room in your house (except for the kitchen and bathrooms).
    [Edited by JoeSix on 07-26-2005 at 02:53 PM]
    24X30 without a filter in the grille,25X40 with one in it.
    With a return that small did you have a five ton system before ??
    What size duct connects to the grille and the furnace/air handler??
    Jul 2005
    To be on the safe side, make sure you have at least a total return 10% minimum larger than the supply total.
    Example; If 400 sq in supply out, you need a min. of 440 sq in return.
    Jul 2005
    The grill is a stamped grill with a filter in it 20"x25" and the duct is a 16" round.
    Jun 2000
    N. W., IN
    Frown
    16" return duct for 5 ton a/c.
    All together now, "not gonna' work"
    Jul 2005
    It's been like this since 1976 and I'm making some changes. Don't want to dump to much into it cause I'm going to try and sell the place in the next 1-2 years.
    Yes it was a 5 ton previously.
    What's your thoughts on the duct size? 20"?
    Thanks for all the input.
    If any of you are in the Spring, TX area, let me know.
    It appears the airbox gets reduced down to an 18" square inlet to the furnace and then 16" round duct to the return air. Not sure I'm calling these things right, but hopefully you know what I mean.
    Thanks again!
    [Edited by bubstang on 07-26-2005 at 04:53 PM]
    Feb 2005
    If you weren't wanting to put much money into it then why did you invest more for a higher SEER that won't work with your return?? You could have put in a lower SEER and did the duct repair for probably close to the same price. I understand you not wanting to put much money into it, but it is a case of either working, or not. In my opinion you don't have a choice as to whether or not to spend more money to fix the return. Eiether you just paid for a new system that will work, or won't work. You choose. It is a no brainer.
    Jun 2000
    N. W., IN
    20" would be a good idea. In Texas that must be one hard working system.
    Jun 2002
    Wow. Even if you could make that work, that's an air speed of 24 ft/second through that duct at 2000 CFM.
    (Not to mention 10 ft/second through that grill opening)
    Whooooosh!
    Jul 2005
    You guys want pics?