Thread: PID wound up?

  1. #1
    Join Date
    Oct 2009
    Posts
    983
    Post Likes

    PID wound up?

    I have a building with several air handlers with an NAE and UNTs controlling the equipment. Two compressors are short cycling in the AHUs. These two AHUs are identical to two others that are working fine. The same program and everything else with the exception of some parameters. Im just wondering if the PID in the UNT needs to be reset. That's the only thing I can think of to fix the problem. Any other thoughts or suggestions? TIA

  2. #2
    Join Date
    Jan 2008
    Location
    Near Philly
    Posts
    546
    Post Likes
    Quote Originally Posted by Igotworms View Post
    I have a building with several air handlers with an NAE and UNTs controlling the equipment. Two compressors are short cycling in the AHUs. These two AHUs are identical to two others that are working fine. The same program and everything else with the exception of some parameters. Im just wondering if the PID in the UNT needs to be reset. That's the only thing I can think of to fix the problem. Any other thoughts or suggestions? TIA
    Set all of the parameters to the same as the one that is working ok. Check the sensor that's being used for the controlled process variable, to see if it's swinging up and down erratically.

  3. #3
    Join Date
    May 2008
    Location
    Mid-Atlantic
    Posts
    35
    Post Likes
    Couple of things... 1st Look in the BO object in the UNT itself to see if you have the min on/off times and interstage delays set up this will help with cycling. Is your cooling command going up and down at a fast rate in Hpro? If so check the prop and intergration times. you don't mention what stragety you are using. Is it possible that your controlling sensor is in a poor location as opposed to the other ones? IE: discharge control and the sensor is right up against the cooling coil!

  4. #4
    Join Date
    Oct 2009
    Posts
    983
    Post Likes
    Thread Starter
    Quote Originally Posted by Dynawiderider View Post
    Couple of things... 1st Look in the BO object in the UNT itself to see if you have the min on/off times and interstage delays set up this will help with cycling. Is your cooling command going up and down at a fast rate in Hpro? If so check the prop and intergration times. you don't mention what stragety you are using. Is it possible that your controlling sensor is in a poor location as opposed to the other ones? IE: discharge control and the sensor is right up against the cooling coil!
    This cooling stage is being controlled by a one stage sequencer in Hvacpro. The cooling prop band and intrgral times seem ok, the cooling command ramps up pretty slow. The min on/off times are the same as the ones that are working properly but im probably going to change them. As far as zone sensor location and DA-T go ill have to check, that's really the only thing left to look at since I have only been looking at trends and programming.

  5. #5
    Join Date
    Oct 2009
    Posts
    983
    Post Likes
    Thread Starter
    also, this is programmed as a 100% OA single path AHU with room control cooling/room reset

  6. #6
    Join Date
    Mar 2011
    Location
    Manitoba, Canada
    Posts
    115
    Post Likes
    You check the HvacPro program. You say you have two stages of cooling but only one output defined in a sequencer. Check the Q/A in the cooling section and see if only one cooling stage is defined. If you have two stages change it to two. If you are doing room control of the cooling you may need to confirm the room setpoint, propband, deadband to determine if they are not too tight. Also make sure you don't have air blowing on the room sensor.
    Hope this helps.

  7. #7
    Join Date
    Oct 2009
    Posts
    983
    Post Likes
    Thread Starter
    Quote Originally Posted by Froz'ninWpg View Post
    You check the HvacPro program. You say you have two stages of cooling but only one output defined in a sequencer. Check the Q/A in the cooling section and see if only one cooling stage is defined. If you have two stages change it to two. If you are doing room control of the cooling you may need to confirm the room setpoint, propband, deadband to determine if they are not too tight. Also make sure you don't have air blowing on the room sensor.
    Hope this helps.
    The way I typed it is confusing. There are two AHUs with the problem. Both AHUs have only one stage of cooling. I think the zone sensor may need to be relocated, since the PID parameters seem to be ok

  8. #8
    Join Date
    Apr 2007
    Location
    Ontario Canada
    Posts
    171
    Post Likes

    The integral may be the problem...

    Quote Originally Posted by Igotworms View Post
    The way I typed it is confusing. There are two AHUs with the problem. Both AHUs have only one stage of cooling. I think the zone sensor may need to be relocated, since the PID parameters seem to be ok
    Every manufacturer writes PID controls, but they don't cross over well.

    I find a UNT will want to see a I value of 600 to 1000. Or none at all for a single compressor.

    D.

  9. #9
    Join Date
    Jan 2008
    Posts
    78
    Post Likes
    Remember that the IT in ASCs are in seconds so you should have a big number for room control, like +/-600.

  10. #10
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    2,660
    Post Likes
    Igotworms,
    Upload the controller, set your HVAC-Pro to generate *.prn and *.ddl files, use long form print format and email all 4 file to me. I think I know what your problem is but it will take too much typing to explain but 2 minutes to find/fix.

    BTW, Integration (IT) is in "Ticks" not seconds. 1 tick is aprox. 1.5 seconds. Found that out the hard way because of a very anal (EPITA) engineer during commissioning.
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)

  11. #11
    Join Date
    Jul 2009
    Location
    Westside
    Posts
    2,083
    Post Likes
    If two units are working fine with virtually the same program, I can't help but think something other than controls. What is the delta T across the evaporator, airflow maybe?. I have seen many UNT'S setup this way resetting discharge and without the absolute correct setup they will short cycle like crazy and usually a compressor death!!.Remember that evaporator needs a good load on it which will provide longer run cycles, if you have say 65 degrees air on the evaporator and you start cooling cycle, and your DAT set point is say 55 degrees it will take no time to reach set point, IE short cycle. Now with minimum on time you can sometime stop that a bit, but that usually drives the DAT really low which in turn drives the suction pressure down also. I personally don't care for DAT reset with DX, if you read one of my other post I explain in detail why, that instance I was explaining was a unt with DX also, that system ate three compressor before I was asked to look at it. I found a short cycling mess with that one also!!. So good luck .

  12. #12
    Join Date
    Apr 2011
    Posts
    14
    Post Likes

    Is it possible that this is not a control problem

    But rather a refrigeration system problem ???

    Is there Hot Gas Bypass ??
    Are the systems charged correctly ??
    Are the TXV and other refrigeration components set-up correctly ??

  13. #13
    Join Date
    Oct 2009
    Posts
    983
    Post Likes
    Thread Starter
    I dont think it is a mechanical problem because I can see the trends at the NAE. The controller is calling it on and off.
    Norriski Tech - The cooling is not being controlled off of DA-T. That is only for the heat, the cooling is looking at the zoom sensor.

    After troubleshooting, I think the zone sensor is faulty. Its located in a good spot but for some reason its reading fluctuates too much causing the PID to go up and down too fast. Thanks for all the input.

  14. #14
    Join Date
    Feb 2009
    Location
    Northeast
    Posts
    587
    Post Likes
    Quote Originally Posted by Igotworms View Post
    ... I think the zone sensor is faulty. ... ... its reading fluctuates too much ...
    Bad cabling can cause this behavior too. Often we have changed the sensor, The problem seems to go away for a while then comes back. ( I think wiggling the wires may make the cable work for a while.) PIA but after the sensor is replaced we usually change the wire next. Controllers are too expensive to change when that usually does not cure a problem like this.

    Bill

  15. #15
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    2,660
    Post Likes
    Igotworms,
    Check your wiring connections and...

    You've got mail !
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •