TAC Jace and a BellyUp Contractor
Hopefully someone can help! I have an older TAC UNC jace that a contractor installed in '06. I have inherited this site due to the contractor going under. I have a back-up copy of the database but it is not in the same format of any of my other JACE databases. The only common theme is a config database file. Is this R2? I am not familiar with that version. Is there any way to convert this. The system level password is gone and the only access is with the web interface and a user level password. Any help would be GREATLY appreciated.
-
04-26-2011, 08:18 PM #2
New Guest
- Join Date
- Jul 2010
- Posts
- 3
Look up the model # for that JACE and see if it is possible to reset the administrative password by using serial shell, if it is an R2 JACE you will need the right version of the software. To connect andake Amy programming changes: I can't remember if TAC had any license restrictions on there branded JACE's
-
05-01-2011, 09:38 AM #3
Regular Guest
- Join Date
- Sep 2010
- Posts
- 45
If it's a UNC then it's R2. The config file is the backup of the station on the UNC, it does not include the images, etc. that may have been added, the db file is the file that will let you run the database on on your laptop, it is the same as the cfg just converted, you can convert either to an xml file with R2.
There is no conversion that I am aware of to convert it to AX. The customer can probably send the DB to TAC and have the password unlocked but if you have no experience with R2 it isn't going to do you much good as you will need R2 on your laptop in order to access it, R2 is a lot different than AX.
If you want to find out what rev of R2 it is running, go to your browser address bar and type in
http://localhost/prism
Where localhost will need to be the IP address of the UNC.
If you want to send it to me I will take a look at the password thing, I can usually get past it.
-
05-02-2011, 02:59 PM #4
Regular Guest
- Join Date
- May 2008
- Location
- Mid-Atlantic
- Posts
- 35
Thanks mikeSands02, I thought R2 was different but I did not realize how different. Do you know of a good way to intergrate this JACE into a JCI FX60 Platform? I have a 60 in place doing another part of the building that was just installed . Is that a possibility? It would be great if you could help with the access. How do i get a hold of you?
-
05-02-2011, 05:11 PM #5
Professional Member
- Join Date
- Feb 2008
- Posts
- 36
You could just replace the UNC with a JACE-6 but would still need the programming software for the field devices. If you have that then you could reverse engineer the SOO for the equipment. Still a lot of programming ahead to get it on AX but doable. Helps if you already have templates designed.
-
05-02-2011, 08:26 PM #6
Regular Guest
- Join Date
- Sep 2010
- Posts
- 45
-
05-02-2011, 08:28 PM #7
Regular Guest
- Join Date
- Sep 2010
- Posts
- 45
Oh how convenient this place is, no PM's, and I thought I was out of kindergarten, just add aol to my name .
-
05-03-2011, 12:54 AM #8
PM's come w/Pro Membership
"How it can be considered "Open" is beyond me. Calling it "voyeur-ed" would be more accurate." pka LeroyMac, SkyIsBlue, fka Freddy-B, Mongo, IndyBlue