York LCH130 Pressure drops
I am trying to find the water flow pressure drops for a York LCH130W-17BA Chiller. Can anyone direct me or have the info. York (Johnson Controls) never responds
Thanks
-
04-28-2011, 09:52 AM #2
Regular Guest
- Join Date
- Aug 2009
- Posts
- 52
which flow pressure?condenser or evaporator?
-
04-28-2011, 10:00 AM #3
New Guest
- Join Date
- Apr 2011
- Posts
- 3
My biggest issue is with the evaporator
It appears from the pump plates they are flowing 280 gpm on both the evaporator and condenser. Not much to go on from a system this old
Thanks
-
04-28-2011, 10:03 AM #4
Regular Guest
- Join Date
- Aug 2009
- Posts
- 52
i know the chillers are very old models i just check my documents and i saw that i dont have have this type but i have the newest type just give me a few to tell you
-
04-28-2011, 10:19 AM #5
Regular Guest
- Join Date
- Aug 2009
- Posts
- 52
i check, but from my experiences on the condenser should have something between 30-50 Kpa dp and the cooler should work between 40-70 Kpa with ideal for me the 60 kpa on cooler pressure drop, i am really sorry that i cant give you also how many l/s value because i dont have the original manual from this type i have the newest ones and i dont want to give you wronge data, hope some on else that have this details can give it
-
04-28-2011, 10:27 AM #6
Regular Guest
- Join Date
- Aug 2009
- Posts
- 52
some more information just i found, for the condenser the limitations are between 3,6-7,2 l/s per 100kw