Results 1 to 3 of 3
Thread: heat problems
    Jul 2005
    Angry
    I hope someone can give me an opinion on this. I am working on 3 ton Carrier ac only, cupe tube metering device, the low side reads 75-80 and the high goes from 230-450 before the overlow turns off the machine. The inside discharge is 72f outside temp. is 97f. the evaporator fan is working the same as the condenser (this one is unusual because it is a squirl cage) thank you for any help.
    Jan 2003
    Kansas City
    outdoor coil dirty==condenser fan motor rotating backwards--recirculating discharge air at condenser--unit surrounded by or covered by a deck--+_+_+_+_+_+_+_+_+
    Hammond
    superheat? subcooling? cfm? wet bulb? dry bulb? dictionary?
    I don’t always drink beer, but when I do I prefer Dos-Equis. I am the most interesting man in the world. Stay thirsty my friends.