Page 1 of 3 123 LastLast
Results 1 to 13 of 29
  1. #1
    Join Date
    Apr 2011
    Location
    Erlensee/ Hessen Germany
    Posts
    10
    Post Likes

    York Chiller Password

    i need the password for york chiller: (service)passcode

  2. #2
    Join Date
    Feb 2010
    Location
    Ontario Canada
    Posts
    1,341
    Post Likes
    C-A-L-L- A- P-R-O-.........

  3. #3
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    spell Y O R K on your phone keys ....................# # # #
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  4. #4
    Join Date
    Feb 2006
    Location
    SouthEastern Virginia
    Posts
    1,077
    Post Likes
    sorry but New Guests do not have these privileges.
    It might get loud!

  5. #5
    Join Date
    Dec 2002
    Location
    atlanta ga.
    Posts
    145
    Post Likes
    there is two, 9675 and 1380

  6. #6
    Join Date
    Apr 2011
    Location
    Erlensee/ Hessen Germany
    Posts
    10
    Post Likes
    1380 and 9675 do not work. Is there a different password?

  7. #7
    Join Date
    Dec 2002
    Location
    atlanta ga.
    Posts
    145
    Post Likes
    what type of york chiller is it and what panel

  8. #8
    Join Date
    Apr 2011
    Location
    Erlensee/ Hessen Germany
    Posts
    10
    Post Likes
    YCWJ and Millennium Recip Chiller Panel.


    How do I get to the programming level? Maybe I'm doing something wrong?

  9. #9
    Join Date
    Dec 2002
    Location
    atlanta ga.
    Posts
    145
    Post Likes
    7396

  10. #10
    Join Date
    Apr 2011
    Location
    Erlensee/ Hessen Germany
    Posts
    10
    Post Likes
    Thank you very much.

  11. #11
    Join Date
    Apr 2011
    Location
    Erlensee/ Hessen Germany
    Posts
    10
    Post Likes
    Can be adjusted so that the head pressure? The machine was switched to a different refrigerant.

  12. #12
    Join Date
    Dec 2002
    Location
    atlanta ga.
    Posts
    145
    Post Likes
    you can program the discharge pressure cutout and the discharge unload setpoint. you will still have the mechanical high pressure switch in the circuit. you can set the cutout for r-22 from 200-399psig and r134 128-275 psig the unload you should set 20-25 psi below the cutout setpoint. good luck my friend.

  13. #13
    Join Date
    Apr 2011
    Location
    Erlensee/ Hessen Germany
    Posts
    10
    Post Likes
    Do you have a manual about it. Perhaps for the panel?

    The change is from R22 to R422D. This refrigerant is not known to you. R22 is banned in Germany / Europe.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.
Comfortech365 Virtual Event