I've got a carrier 58uhv100-1-20 furnace 115v going to the motor threw the what looks like a transformer both sides and no action and no codes on the board ,Bad motor? am I missing any thing Thanks in advance T
[Edited by texas t on 07-24-2005 at 12:54 AM]
"A man who carries a cat by the tail learns something he can learn in
no other way." 
-Mark Twain, American writer (1835-1910)
-
Here's the manual: 58UHV Troubleshooting
Start on page 8 and follow the steps. You won't go wrong.
BTW, that transformer looking thing is a line choke to keep the variable speed noise off the home's electrical system.
-
jrbenny, Thank you ALOT