    What are the formulas for calculating cfm on oil,natural gas and LP furnaces? Btu input x ? divided by 1.08 x delta T
    Apr 2002
    CFM=OUTPUT/(1.08 x delta T)
    Clock the furnace, measure efficiency to get output
    The way we build has a greater impact on our comfort, energy consumption and IAQ than any HVAC system we install.
    http://www.ductstrap.com/
    South/West of Quebec in the other part of Canada
    here is another one for you..Electric furnace...
    volts x amps x 3.14 = btu output
    btu output/ 1.08 x temp rise