    When a 3 1/2 ton Evap. is installed with a 3 ton condensing unit........

    (piston type metering device)


    Do you use piston for 3 or 3 1/2 tons ??

    Don't you always use the piston that matches the cond. unit?

    If so,,,,,

    There's still only the amount of refrigerant flowing in the evap. coil as a 3 ton........

    Why bother with installing the 3 1/2 ton evap. coil if you only use a 3 ton piston??

    Thanks.......

  2. #2
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    34,339
    Use the piston that came with the outdoor unit. Oversized evap increases sensible and SEER slightly so may have to do that go get the rated SEER. Decreases humidity control, not something to do in a steamy climate. Same cooling over larger surface area means warmer coil.

  3. #3
    Join Date
    Apr 2003
    Location
    GA/SC
    Posts
    360
    So it increases the sensible heat removal and decreases the latent heat removal ??

    Why would a contractor want to do this while installing a new system?

    Just to increase the seer rating ?

  4. #4
    Join Date
    Dec 2002
    Location
    Houston,Tx.
    Posts
    16,077
    They should be using a TXV coil if there using a larger coil to get a certain seer rating.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards". - Vernon Law

    "Never let success go to your head, and never let failure go to your heart". - Unknown