    If one decides to lower the cfm per ton in hope to achieve better humidity removal (say from 400 to 325cfm per ton), should the charging system be rechecked/adjusted to manufacturers spec afterwards or do you leave it at its defaulted original setup (400cfm)...unit 14seer Ruud w var speed fan coil w/txv....
    Respectfully yours,
    Apr 2004
    Altering the airflow generally alters the charge. If you have a TXV its probably not a problem. Remember the factory charge is for the unit, 25' of lineset, the coil and 400 CFM. A piston system should be safe but should be checked.
    Jul 2005
    south
    try addinng a humidistat to maintain humidity. humidistat can be wired to turn on 1 stage of electric heat to force ac operation withot overcooling space temp. i have done this in several commercial applications and it works great
    SW Wisconsin
    Respectfully yours,
    The proper sizing of the A/C system is the most critical factor to achieve sufficient runtime to bring humidity down.
    With adequate runtime 350-cfm per ton should do the job.
    No problem with the charge with the TXV, as you may want to ramp up to 400-cfm per ton again.
    http://www.udarrell.com/ac-trouble-s...ubcooling.html