JCI VA-7820 or 7830 (valve actuators)
Has anyone had experience with these actuators failing because they indicate losing control signal? I have had several do this and the signal is always present.
-
04-21-2011, 12:30 PM #2
Banned
- Join Date
- Mar 2006
- Posts
- 3,641
Blue capes and proper pid tuning save actuator lives.
-
04-21-2011, 01:36 PM #3
Professional Member
- Join Date
- Mar 2011
- Location
- Manitoba, Canada
- Posts
- 102
I have had issues with other JCI actuators and the solution was to reset the 24Vac. The electronics in the actuator were "locking up" and there was a recall placed on the parts. This was a couple years ago on a M9216-HGA valve though. Could be going down the same path. If you have a relationship with the local branch try them and see if they now of a problem. Otherwise try Milwaukwee on the 800# and see if you can get somewhere.
-
04-22-2011, 02:50 PM #4
Regular Guest
- Join Date
- Nov 2008
- Location
- Colorado
- Posts
- 6
Froz:
You are correct in that the 24vac removal resets the actuator. But that does not bode well in an automatic control application. I was looking to see if your second part is true that possibly a manufacturing defect is out there since I have some actuators that do not exhibit this symptom.
Freddy:
I took the blue cape off and replaced it with a real superman suit. Glad to know that blue blood runs in your veins though. LOL: