    Triple Evacuation

    As and HVAC student reading a book from the field I learned about the concept of triple evacuation today. Im a little confused as to why this is necessary. It seems to me that you evacuate once and the system should be good but letting some trace refrigerant back in and evacuating again and then repeating it yet again? What is the purpose? Im sure there are plenty good reasons out there and as a dumb student I'd love to know them.

    Thanks.

  2. #2
    Join Date
    Oct 2001
    Posts
    6,956
    triple evac was before the epa cert/micron days kicked in when you burped the vac with the systems freon then revac'd it...now the microns below 5000 are considerd moisture and as it dries up you start passing thru into 4000,3000,2000 and 1000 microns mint vacs are 500-250 micron range and let it sit for 4 hours/if you can't get below 5000 microns at the start there is a leak.........
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  3. #3
    Join Date
    Feb 2004
    Location
    Western New York
    Posts
    1,047

    Long, long ago...

    Triple vac and purge with refrigerant was back in the day when we blew out condensers with R-12 (legally OK).

    How old is that textbook?
    Experience is what you have an hour after you need it.

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    18,249
    Quote Originally Posted by baub View Post
    Triple vac and purge with refrigerant was back in the day when we blew out condensers with R-12 (legally OK).

    How old is that textbook?
    It is probably subtitled: "Working with GE air conditioners."
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist

    AOP Forum Rules:







  5. #5
    Join Date
    Mar 2011
    Location
    East Coast FL
    Posts
    1,058
    Me thinks GE air conditioners were fantastic.

    If somewhat difficult to service.

    No one I know triple evacs any more.

    Nitrogen pressure test , release nitrogen , evacuate with micron gauge.

    New method.

  6. #6
    Join Date
    Mar 2001
    Posts
    1,486
    Theory was that the addition of refrigerant to an evacuated system would let the refrigerant help carry contaminents out of the system during second and third evacuation. Kinda like a "Purge". Not practiced these days because of CFC restrictions.
    One way to outthink people is to make them think you think. They'll think you're not really thinking what you're trying to get them to think you think...........

  7. #7
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,550
    Quote Originally Posted by uniservice View Post
    Theory was that the addition of refrigerant to an evacuated system would let the refrigerant help carry contaminents out of the system during second and third evacuation. Kinda like a "Purge". Not practiced these days because of CFC restrictions.
    The theory of reducing contaminants by breaking the vacuum with refrigerant is still sound, just illegal.

    Even under a deep micron vacuum, there IS still vapor in the system. By breaking the vacuum with refrigerant, you replaced the air or nitrogen with refrigerant, thus reducing the amount of remaining contaminants.

    This may be splitting hairs.

    I normally just pull deep vacuum and recharge as is typical procedure.

  8. #8
    Join Date
    May 2007
    Location
    Dry as a bone Tucson
    Posts
    4,278

    GE

    Quote Originally Posted by AiResearch View Post
    Me thinks GE air conditioners were fantastic.
    Yes they were. Replaced one 6 years ago. Side discharge cfm, gigantic caps.
    Early 70's i think.
    Some Talk, Some Do
    "keeping condensing pressures low and evaporator pressures high"
    "Some customers are more interested in comfort than energy savings"
    Blog
    Web
    Facebook


  9. #9
    Join Date
    Sep 2009
    Posts
    9
    The book I was reading is:

    Refrigeration & Air Conditioning Technology 4th Edition
    by Whitman * Johnson * Tomczyk

    Copyright 2000

    Not exactly the most current issue of this book but still tons of good knowledge. Thanks to you guys for all the help.

  10. #10
    Join Date
    Aug 2009
    Location
    Michigan
    Posts
    88
    Our company's procedure is tripple evacuate (even R-22 systems), we don't use refrigerant, we use nytrogen. We have very few call backs due to leaks (the few we have, I would guess, someone cut a corner somewhere).

  11. #11
    Join Date
    May 2009
    Location
    South of Heaven
    Posts
    1,139
    Mitsubishi City-Multi requires " Triple Evac. " using nitrogen.

    I took my cfc certification a long time ago ( 1993 I think ). At that time it was legal to vent refrigerant for the purpose of " dehydration and leak testing " if I'm remembering correctly.

    I installed a ten ton Aaon split system 2 weeks ago and did a triple evacuation using nitrogen and the results were dramatic ( from the first pump down versus the second ). Using an Appion TEZ-8 pump and 2 micron gauges ( one analog and one digital ) ...the initial evac. was 500 ( pump running ). Broke vacuum to 30 psi nitrogen , bleed out of low side of system to 5 psi. The next evac went down to 200 microns ( pump running ) in a much shorter time than the first. System settled at 350 microns for an hour ( both gauges agreed , I called it good ).

    I can assure you that using refrigerant for this process will reduce evacuation time by at least 1/2 ( if I'm remembering correctly ).
    Last edited by tech45; 04-22-2011 at 11:00 PM.

  12. #12
    Join Date
    Mar 2011
    Location
    East Coast FL
    Posts
    1,058
    Pretty sure the text books state that dry nitrogen has a higher moisture absorbtion than a refrigerant , however some refrigerants are great solvents for removing other contaminants. Just depends on the situation. Cant go wrong with nitrogen and a micron gauge IMO.

  13. #13
    Join Date
    Mar 2011
    Location
    East Coast FL
    Posts
    1,058
    Quote Originally Posted by ACFIXR View Post
    Yes they were. Replaced one 6 years ago. Side discharge cfm, gigantic caps.
    Early 70's i think.
    One could start a whole new thread about GE refrigerating equipment!!!

    The domestic fridge would run forever and ever and ever.

    Neat thing about that company is they made EVERYTHING in the unit. Right down to the wire.

    And their hermetic compressors were workers tougher than a Mack truck.

    Man ive seen those things run under the worst conditions for weeks...

    They really put the good metals in there..


    (sorry for the sidetrack guys)

Page 1 of 2 12 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event