Results 1 to 10 of 10
Thread: size
    Jul 2005
    Question
    First of all I am a homeowner,however I am not trying to install anything just need info.I recently purchaced a home that needs a new furnace and ac.I have had estimates from a few companies to get opinions, not compete on price.The house is a 2000 square foot 2 story home in central Ohio.The problem I am having is sizing.One company gave an estimate for 115000 btu furnace and 3.5 ton ac.One gave me an estimate for a 92000 and 3 ton.The last one was 115000 and 4 ton.I started reading post on here and purchaced the advertized sizing program for 2 months.I plugged in all information for the whole home and the results were 69949 for heat loss and 21478 for heat gain.Knowing this what sizes should I request and how do I explain to the contractor what I did without making them mad?I just want the right size equipment.After all the research I have did on this subject I know this is important and I think these guys are just shooting from the hip on the sizing (none of the contractors measured one thing in the house they all did a walk through).Please help.
    SW FL
    Originally posted by s34251e
    The house is a 2000 square foot 2 story home in central Ohio.The problem I am having is sizing.One company gave an estimate for 115000 btu furnace and 3.5 ton ac. ...
    I plugged in all information for the whole home and the results were 69949 for heat loss and 21478 for heat gain. Knowing this, what sizes should I request and how do I explain to the contractor what I did without making them mad? I just want the right size equipment.
    Designer Dan
    With those kind of numbers, I'd probably shoot for around 70K output on my furnace and 2.5 ton A/C. I don't like to cut the air real close, like putting 2 ton in, just because most 2 ton units are less than 24,000. I'd like a little reserve. If you like it cold, 3 ton wouldn't be so bad because it would run enough to dehumidify. Beyond a 3 ton is nuts.
    We put a 2.5 ton in a 2500+ sq ft 2 story here in Indy last month I asked the salesman if he was nuts, looked like way too little for the big east-west facing home. He inspected the job this week on a very hot, humid day. Complained about how cold they had it in there. Don't let anybody come in here and tell you so many sq ft per ton crap. It doesn't take a monster A/C to cool a well built (midwest/ohio valley type construction) home.
    SW FL
    Exclamation Experience
    The house is a 2000 square foot 2 story home in central Ohio.The problem I am having is sizing. One company gave an estimate for 115000 btu furnace and 3.5 ton ac. ...
    I started reading post on here and purchased the advertized sizing program for 2 months.
    I plugged in all information for the whole home and the results were 69,949 for heat loss and 21,478 for heat gain. Knowing this, what sizes should I request and how do I explain to the contractor what I did without making them mad? I just want the right size equipment.
    R-30 Ceiling ?
    R-19 Walls ?
    Attic Temp ___ ' F
    Design Temp ___ ' F
    What is the total area ___, U-value ___
    and S.H.G.C. ___ of the windows?
    _______Glass Load = _,___ BTUh
    _____Ceiling Load = _,___ BTUh
    _______ Wall Load = _,___ BTUh
    Infiltration load = _,___ BTUh
    __ Internal Gains = _,___ BTUh
    (Lights, Computers, Kitchen, TV, ...
    ______Duct Losses = _,___ BTUh for R-___
    ______ # of people
    ______People Load = _,___ BTUh
    ____________ Total __,___ BTUh
    21,478 BTUh seems VERY, VERY Low for 2,000 Sq. Feet
    Designer Dan
    80,000 90%, and 2.5 ton, by your calcs.
    Jul 2005
    Dan I agree it sounds low.I am sorry I can not give you all the info you ask for.I used the hvac-calc program and put in all info I was ask.The isulation is r-13 for the walls and 19+ for the cieling and r-4 in ductwork.This will probably not help you, but thank you for replying.
    SW FL
    Question Cold
    ... He inspected the job this week on a very hot, humid day.
    Hopefully, it was < 80'F.
    Designer Dan
    SW Wisconsin
    This is how I would select the tonnage to install if it were my own home.
    Columbus, Ohio summer design: 90 dry bulb, 73 wet bulb, approx 44% relative humidity. If your heatgain is accurate, 21478 is a 1.8 ton heatload. A manual J with 15% oversizing gives you 2.07 tons, equipment selection says a 2-ton condenser with a matching "TXV metered" evaporator coil.
    I personally would go with the 2-ton; the duct system must be perfectly sized, well insulated, with NO air leaks! If it has any problems keeping up, "there are always many things you can do to reduce the heatload; think about it." I would rather have my A/C slightly undersized than oversized.
    Walked through and told you 4-ton, when the manual J, if accurate, calls for 2-ton by the approved sizing protocol.
    http://www.udarrell.com/proper_cfm_b...g_systems.html
    Is the furnace oil or gas? The large heat exchangers in most Oil furnaces can create airflow problems unless you keep the coil high enough above the furnace with usually a transition reducer.
    http://www.udarrell.com/oil-heating-airflow-test.html
    AOP Forum Rules:
    Rules for Posting
    Rules For Equipment Owners
    Equipment Owners Find a Contractor HERE!
    Free online whole house load calculator & Sizing: http://www.loadcalc.net/ Anyone can use it...!
    udarrell
    SW FL
    AT LEAST 2.5 straight or
    preferrably 2-stage 3 ton
    is needed.
    2.5 ton provides ~22,000 BTU Sensible.
    Designer Dan
    What design temps did you use??What city/state??
    Just call around for estimates ,insisting on a manual J,then when they do one ,they should have no promlem looking at yours ,to compare the results.Keep dialing some one there knows how.
    Try http://www.acca.org for a contractor.Or the manufacturers websites for the top dealers.