That's if you have chillers. Also that's why we tied in the BMS input for alarming/monitoring purposes w/trends.
The biggest issue I found is once it was tied into the BMS the guys seemed to think it would alarm when there was a problem, and forgot about other parts of the system that weren't tied in yet. It does alarm if it can see it but it doesn't take place of regular maintenance.
BTW - the once a month is a forced/documented re-cal of the sensor and zeroing it out. Towers are 'supposed' to have a basic inspection weekly.